Hi Ray,

I guess my answer is that its way easier to switch one button with easy access 
than go deep into the menus and have to change 4 inverters.  
This situation is a short term thing.  In this case it is an issue as the 
generator cannot handle both the chargers and the load. And he doesn’t want and 
I agree to have an additional cycle on the batteries when they don’t need it.

I’m working with OB to find out why this is happening.  

Thanks

jay

peltz power
  
> On Apr 29, 2016, at 11:07 AM, Ray Walters <r...@solarray.com> wrote:
> 
> What's wrong with the chargers being on?  Just set the charge settings 
> (absorb 56 v, and absorb time 5 minutes) fairly low. It will lightly charge 
> for a few minutes, and then go to float.
> Just because your customer imagines this to be a problem, doesn't mean it 
> actually is.  Its not going to hurt the batteries or use excessive fuel to go 
> through a little refresh charge like this, and if the batteries actually are 
> low, these charge settings will be helpful.
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> 
> On 4/29/2016 11:56 AM, Darren Emmons wrote:
>> When the generator is auto started, the inverter's charger will be enabled. 
>> After the generator is stopped, the inverter's charger will be returned to 
>> the mode before the generator started. The logic is if you are running the 
>> generator the Inverter's charger should be enabled. You could lower the 
>> charger AC limit to 0 Amps.
>> 
>> 08:00 Inverter charger OFF
>> 10:00 Must run start -> charger ON
>> 11:00 Must run stop -> charger OFF
>> 
>> >Darren
>> 
>> 
>> On 04/27/2016 05:31 PM, jay wrote:
>>> HI All,
>>> 
>>> I’ve got a problem that outback tech hasn’t been able to figure out.
>>> 
>>> off grid system
>>> mate 3
>>> quad stacked VFX 3648
>>> 
>>> The generator is set to specific start/stop daily timer.  This works fine.
>>> 
>>> The client has plenty of solar for the day, and when he runs his generator 
>>> he doesn’t want the chargers to operate.
>>> OK so just hit charge off, and yes the chargers will turn off.
>>> 
>>> But next day, genny starts up, and the chargers come back on as well.
>>> 
>>> Outback says that shouldn’t be happening, but it is.
>>> 
>>> Anybody have this issue or know of a fix?
>>> 
>>> Thanks
>>> 
>>> jay
>>> 
>>> peltz power
>>> 
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>>> 
>>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to