Dear Fellow Wrenches


Below is a design conundrum that may resonate with some of you:



We are finalizing a design for an off-grid residential system.  The
customer insist the PV should be on the roof and pre-installed a 1-1/4” PVC
conduit from his roof to a crawl space, in anticipation of a solar
install.  This created real problems, because we all know we can’t pull PV
source or output circuits in (or now, on)  the envelopes of habitable
buildings.



There was no practical way to replace the PVC.  We contrived a method to
sleeve ¾” liquid-tight through the 1-1/4” PVC to the crawl space,
continuing on with EMT.  This is the largest metallic conduit we could
fit.  The distance was greater than 10 feet so we couldn’t use EMT.  Due to
the conduit size restriction, we upgraded to Morningstar 600 volt charge
controllers, allowing us to reduce conductor size.



(As a sidebar, although the Morningstar is listed as a 600 volt charge
controller, we have found no circumstance were we could take advantage of
that high a voltage.  With the currently available high wattage modules, by
the time we added enough in series to get to 600 volts, we were well beyond
the wattage capabilities of the controller.  For sake of design
considerations, I suggest one regard these units as ~300 volt charge
controllers.)



We now have plans for 300 volt PV feeders running down an interior wall and
under the house, with no roof-top disconnecting means.  It is my
understanding none are required.  I am not comfortable with this.  In this
scenario, there is no safe way to replace either of the two Morningstar
controllers. Should someone drill through or damage the EMT in the wall or
under the floor, there would be no way to turn off the feeder.



I don’t like putting HU361RBs on a roof.  They must remain vertical and so
they stick up too high and are hard to provide mounting for.  Sola-deck
units are another option, but they require integrating with shingles, not
practical on this job or many others.  I finally settled on a DC-Sunvolt
PV-X16A-4X-RG disconnect as a possible solution.  At $216 it is not out of
range.  The unit will provide means to turn off the feeders for service.  I
will report back on my impressions of the unit.



To distill this scenario, I don’t believe the code requires a disconnect,
but I feel morally obligated to install one.  I’d be interested in
verification of the code interpretation and others response to similar
situations.



I found no other options for rooftop disconnecting means that would be
small, reasonably priced and not present a high profile.  If there are
products I don’t know about, I would be most grateful to receive your input.



While researching the hardware I stumbled upon this article, linked below.
It seems to present a real dilemma, but I am not convinced.  Please remain
skeptical as you read.  It appears all of the links direct you to the same
source.



https://www.linkedin.com/pulse/greatest-debacle-solar-pv-australias-rooftop-dc-isolator-lucas-sadler



Thanks again to all of you for helpful advice and expertise.  I learned
about Sunvolt here, just one of many great suggestions.



Sincerely,



William Miller





[image: Gradient Cap_mini]
Lic 773985
millersolar.com <http://www.millersolar.com/>
805-438-5600
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to