Hey Jay,

        From what I've heard form battery manus, the C rates likely even in a 
well PV-ed system still will not produce C-rates high enough to approach a high 
or "longevity reducing" internal battery temp, assuming a typical bulk, absorb, 
float cycle.  Of course, battery environmental location (typical temps) would 
set a baseline from which batt temp would rise from.  Here in the Sierra, 
ambients are not very high 95% of the time.

        Just curious, how does the wiz bang account for all loads...2 shunts?

Thanks,

Bill
Feather River Solar Electric
  ----- Original Message ----- 
  From: jay peltz 
  To: RE-wrenches 
  Sent: Thursday, May 21, 2015 8:07 PM
  Subject: Re: [RE-wrenches] FLA battery setpoints with larger arrays


  Hi Allan,


  I like the classic/wiz bang jr.  This allows really good end amp control as 
all loads are accounted for.


  Higher C rates equal higher internal temps which definitely will shorten the 
life.



  On Thu, May 21, 2015 at 10:56 AM, Allan Sindelar <al...@sindelarsolar.com> 
wrote:

    Wrenches,
    In the last few years I have changed my approach to off grid system sizing, 
primarily due to higher battery costs and lower module costs. Rather than 
shooting for a traditional 80-90% of winter load profile target, I will size a 
larger array and smaller battery bank, figuring (especially here in the sunny 
Southwest) that batteries will recharge more quickly, will spend more of their 
time full (and thus last longer), and will be at least partially charged during 
cloudy weather. This even allows for smaller battery banks that are cycled more 
deeply (as long as there's a backup gennie in the mix); the lower cost of a 
smaller size may allow for a set of higher-quality industrial cells.

    I first began to rethink my design approach after reading Christopher 
Freitas' Solar Pro article on large battery banks a few years ago. Being able 
to refill in a day was part of his strategic approach to battery bank design. I 
used and wrote about this approach in my tiny house article in the current Home 
Power. However, I'm just beginning to get owner feedback about greater water 
consumption and the need for more frequent watering. This is especially the 
case when I add array to an existing system, and the old watering schedule is 
suddenly not enough. 

    When I design new systems I now encourage larger arrays and smaller battery 
banks, as the batteries spend more of their time happily full and recover more 
quickly after a discharge period. But I am thinking that I will have to begin 
changing charging setpoints in response. Flooded batteries have a range of 
recommended bulk setpoints, from 28.8 to 29.6 volts on a 24V system. When 
arrays were smaller we set to the higher end of the range to take advantage of 
topping off when available, and a two hour or longer absorption was considered 
beneficial, as long as the CC could transition to float at 2% of capacity or 
so. With a larger array a better approach may be to lower the bulk/absorption 
setting, as well as reduce absorption time and raise the float transition 
current ("done amps"). 

    I'm writing to encourage a discussion among off grid Wrenches. Are you 
changing the relative relationship between array and battery capacities? If so, 
how are you adjusting charge controller setpoint programming? For example, how 
would you program a Midnite Classic, Outback FM or Schneider XW if you could 
achieve a C/10 or C/15 charge rate?

    Thanks, Allan

    Allan Sindelar
    al...@sindelarsolar.com
    NABCEP Certified PV Installation Professional
    NABCEP Certified Technical Sales Professional
    New Mexico EE98J Journeyman Electrician
    Founder (Retired), Positive Energy, Inc.
    505 780-2738 cell








  -- 

  Jay Peltz
  Peltz Power
  jay.pe...@gmail.com


------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Redwood Alliance

  List Address: RE-wrenches@lists.re-wrenches.org

  Change listserver email address & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out or update participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to