All magnum auxiliaries are battery direct ( AGS,BMK) so they drain the battery. 
 
Jay
Peltz power 

Sent from my iPhone

> On Dec 17, 2014, at 10:20 AM, Allan Sindelar <al...@sindelarsolar.com> wrote:
> 
> Corey,
> In a somewhat similar situation years ago: a client had installed a 
> generator/inverter/battery system at an off grid cabin. The system was 
> intended to use the Trace SW4024 inverter to maintain AC to support the 
> generator's battery charger; then send an autostart signal to the gennie, 
> which would recharge the batteries. It was a perilous design, destined to 
> fail, and it did. Once the generator failed to start, the inverter reached 
> low voltage disconnect and some remaining DC load dropped the battery voltage 
> further, to where the inverter couldn't be booted up to recharge the 
> batteries. And of course, without the charger the generator was useless. 
> 
> From the Don't Try This at Home Dep't. Archives: I brought two old 12V 
> batteries with me to the site and set them up in series next to the dead 
> bank. I started the generator, disconnected one battery cable at the bank, 
> ran jumpers from the cables to the two I brought, booted up the inverter, 
> started the charging process, reconnected the disconnected cable, and removed 
> the two old batteries. The inverter continued to recharge the dead bank, 
> although the batteries were permanently weakened, of course, and were soon 
> replaced (and some trickle-charge PV added). Basically I       jump-started 
> the dead batteries as you would do with an automobile.
> 
> I suspect that you could do the same with the Magnum in your situation, and 
> it would be much more effective than 1-2 weeks of slow charging - as in one 
> trip, and the chance to focus your time and effort on the causes of the 
> problem.
> Allan
> 
> Allan Sindelar
> al...@sindelarsolar.com
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
>> On 12/17/2014 10:36 AM, Corey Shalanski wrote:
>> Clarification and Update:
>> - I believe I may have inadvertently thrown Magnum under the bus in in my 
>> initial post. 
>> ᐧ
>> While on site yesterday I did speak             with Magnum's customer 
>> support about my findings and they advised to try to trickle charge the 
>> batteries up to the minimum threshold at which the Magnum inverters would 
>> turn back on. From there we will hopefully be able to run some more 
>> determinate tests. My question about the low-battery-cutout was more 
>> intended to explore whether others have ever experienced any similar issues 
>> with this protection feature. I am finding out that the feature is only 
>> relevant during inverting (not charging) mode and so would imply that the 
>> utility feed had been cut, which does not appear to be the case.
>> - Our battery distributor has lent us a 12-circuit trickle charger - one set 
>> of alligator clips per battery. I am planning to re-visit the jobsite later 
>> today to put each battery on a trickle charge, which I am told will take 1-2 
>> weeks for any lasting change to take effect. The distributor advised to 
>> reverse the leads on the batteries with negative voltage, hoping that they 
>> may be recoverable as "reversed pole" batteries thenceforth.
>> 
>> --
>> Corey
>> 
>> 
>> On Tue, Dec 16, 2014 at 8:27 PM, <cshalan...@joule-energy.com> wrote:
>>> 
>>> 
>>> Wrenches,
>>> 
>>> I visited a customer today whose grid-tied battery backup system suffered
>>> some sort of catastrophic failure, and now I'm trying to play detective to
>>> figure out what happened and whose equipment/design is to blame.
>>> 
>>> Here is what I know so far:
>>> - System is ac-coupled with a Sunny Boy 7000 (7.85kW array), Magnum
>>> MS4448PAE (x2), 3 strings of 4 12v batts (705Ah total)
>>> - Site visit was triggered by the Sunny Boy registering zero output via
>>> online monitoring.
>>> - SPST Solid state relay installed on Sunny Boy output, controlled via
>>> Magnum router, serves as secondary overcharge protection                 to 
>>> Magnum's
>>> frequency shift feature. Technician who initially responded claims he
>>> measured 240v across the relay's terminals - relay manufacturer claims this
>>> is "100% impossible". We removed the relay from the circuit, and the Sunny
>>> Boy is again operational.
>>> - On arrival I found the Magnum display showing a "Low Battery Charge"
>>> message with the bank measuring ~4Vdc. The individual                 
>>> batteries were in
>>> various states of charge, ranging from high of 6.3v to low of -2.6v. These
>>> measurements were taken at rest, all battery cables disconnected, and yes
>>> three of the batts were registering a negative voltage.
>>> - Customer reports that he was not aware of any recent prolonged power
>>> outages.
>>> 
>>> The three potential suspects would seem to be:
>>> - SS relay: The customer is convinced that this is the weak link in the
>>> system and somehow triggered this failure. I am not so convinced but would
>>> be interested to hear recommendations for properly testing its
>>> functionality.
>>> - Magnum equipment: Since there is low-battery-cutout protection, why would
>>> this feature not have activated and prevented the batteries from draining
>>> so low?
>>> - Batteries: I am not very familiar with modes of failure, but our
>>> distributor suggested that an internal short could be a possibility - what
>>> might have triggered this?
>>> 
>>> Clearly I am fishing for potential leads here, so any suggestions are
>>> welcome.
>>> 
>>> Thanks!
>>> --
>>> Corey Shalanski
>>> Joule Energy
>>> New Orleans, LA
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to