There's copper in them thar hills!

You might even be able to buy 1kW of new PV with that.

But is your math wrong? 24 x 80W = 1920W not 960W.

Have you tested these modules? Solarex does not have a great track record. The 
APT PowerCenter puts this back about 20 years, so they aren't exactly young 
modules.

Brian Teitelbaum
AEE Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Dana
Sent: Tuesday, June 04, 2013 3:11 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Old Modules for GIT system?

I forgot to add to add we have 220' of 4 X 4/0 Thhn running to the house. With 
today's prices I could pull that out and purchase a couple of the Enphase 
inverters

____________________________________________________________________________
Dana Orzel
Great Solar Works, Inc -  NABCEP # 051112-136
d...@solarwork.com<mailto:d...@solarwork.com>  - 
www.solarwork.com<http://www.solarwork.com>
O - 970.626.5253    F - 970.626.4140   C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"


From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Steven Lawrence
Sent: Tuesday, June 04, 2013 3:53 PM
To: re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Old Modules for GIT system?

Dana,

Maybe wire 3 in series to a single Enphase?  It'll depend on what the voltages 
are.


Date: Tue, 4 Jun 2013 14:01:42 -0600
From: "Dana" <d...@solarwork.com<mailto:d...@solarwork.com>>
To: "'RE-wrenches'" 
<re-wrenches@lists.re-wrenches.org<mailto:re-wrenches@lists.re-wrenches.org>>
Subject: [RE-wrenches] Old Modules for GIT system?
Message-ID: <05f401ce615e$55773960$0065ac20$@com>
Content-Type: text/plain; charset="us-ascii"

I have a client eat has a 24 - Solarex  SX 80 PV module system that was off
grid, Trace inverter, APT Power panel and an very aged L-16 battery bank.

The utility came in and he wants to go grid tie. It is or was only 960 watt
originally. I realize that an array rewire is in order and it may only be a
1 KW system but he is interested in getting the equipment upgraded.

Has anyone done a grid tie with such a small array and with modules this
old?

Any thoughts on installing sealed batteries and leaving it alone?



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to