In 2006 we installed a dozen Spire 85W modules w/clear backing in pairs as skylights. Shortly after, the building attached to the electrical equipment room, took a direct lightning strike to the wind anemometer 10 feet above the roof. Of the 12 modules four suffered damage to their diodes. Several were completely vaporized, there was nothing remaining except powder and the leads. Others had burnt diodes with leads that had clearly been very hot. Other modules were just fine, the damage seemed to be random with all 12 in series.
The 4 trackers, the closest ~70 ft. away, are grounded with two spools of buried #8 bare copper and Uffer grounds in the concrete piers were untouched. Delta SS's at the tracker discos and in the inverter room were unaffected which I thought was odd. 5 Sunny boys & 2 Sunny Islands in the same room were toasted. Our only experience with lightning. Jim Duncan North Texas Renewable Energy Inc www.ntrei.com <http://www.ntrei.com/> NABCEP PV 031310-57 TECL-27398 nt...@1scom.net 817.917.0527 From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jeff Irish Sent: Friday, September 07, 2012 9:41 AM To: RE-wrenches@lists.re-wrenches.org Subject: [RE-wrenches] Extensive Lightning Damage to Modules A customer of ours has recently suffered lightning damage to 31 out of 160 top of pole mounted modules. This is the first time in 10 years that I've seen modules damaged by lightning. Lots of inverter GF fuses and a few inverters, but never modules. We're trying to determine if it was caused by the lightning flash irradiating the modules or ground currents. The array consists of 16 DP&W top of pole mounts with 10 modules each, arranged in a square of 4 poles E-W and 4 rows N-S. The poles are 13 feet center to center E-W and the N-S row spacing is about 50 feet. The poles are 6 inch galvanized Technoposts, augured 5 - 7 feet into the firm ground, connected with a network of about 160 feet of bare #6 copper and at least 8 copper plated ground rods. Altogether we have about 130 square feet of bare metal surface area connected and buried in the ground at and around the array. The customer saw lightning strike just after dawn a few weeks ago a couple hundred feet to the southwest where it also destroyed two utility pole mount distribution transformers and ran along the utility wires 100 feet south of the array. The inverters are 200 feet NW and suffered no damage. The array and modules look totally fine, except some of the J-boxes are deformed from heat. Opening the J-boxes shows varying levels of damage to one or more diodes, from discoloration to being broken and cracked open. The odd thing is the pattern of damage (we've tested all the modules individually for Voc and Isc). Only modules in the south row of 4 poles are damaged, and the damage is concentrated on the modules closest to the ground; modules higher up in the air appear OK. Also, damage is less frequent as you move east, away from the direction of the strike. If it was caused by ground currents, why would the current want to go up the poles, why only the southern row of poles, and why damage more modules closer to the ground and not those at the top? Is it possible a flash near the ground irradiated the modules causing a current spike and the southern row shielded the other rows from most of the flash? Anyone have experience with this? Jeff Irish, PE President Hudson Solar 13 Hook Road Rhinebeck, NY 12572 T.845.876.3767x110 F.845.876.3912 j...@hudsonsolar.com Solar Electric Systems NYSERDA Eligible PV Installer NABCEP Certified Solar PV Installer NABCEP Certified PV Technical Sales HudsonSolar.com <applewebdata://B5F2562A-2B67-4161-84E4-42F12DC28720/www.hudsonsolar.com> 2011 NYSERDA Excellence in Quality Award | 2011 NYSEIA Award Winner | 2009 Best of the Hudson Valley | 2008 SunPower Dealer of the Year | EDC Business Excellence Award for Innovation
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org