Kent,

Surge protection is at the inverters, 200 feet away, on both the AC and DC 
sides.  Nothing at the array; never thought we'd need it there.  There's a 4 
string fused DC combiner on the west pole of each row; no damage visible on any 
of them and their fuses were all ok.  And yes, each pole of 10 modules is a 
separate DC string, 4 are combined into a DC output circuit to each of four 
SB7000US inverters.

Jeff
Hudson Solar

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent Osterberg
Sent: Friday, September 07, 2012 11:56 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Extensive Lightning Damage to Modules

Jeff,

Is there any surge protection in the combiner boxes? Any damage visible in the 
combiner boxes? Any fuses or breakers open in the combiner boxes? Is each pole 
a single string of modules or multiple strings of modules?

While there where undoubtedly ground currents flowing they probably didn't 
cause the damage in the module junction boxes. The PV module and wiring to it 
form a loop - often a loop with a large area in the vicinity of the module. The 
current from the lightning strike has a tremendous dI/dt and the changing 
magnetic field from it will induce voltages in any wire loop.


Kent Osterberg

Blue Mountain Solar, Inc.

www.bluemountainsolar.com<http://www.bluemountainsolar.com>

t: 541-568-4882


On 9/7/2012 7:40 AM, Jeff Irish wrote:
A customer of ours has recently suffered lightning damage to 31 out of 160 top 
of pole mounted modules.  This is the first time in 10 years that I've seen 
modules damaged by lightning.  Lots of inverter GF fuses and a few inverters, 
but never modules.  We're trying to determine if it was caused by the lightning 
flash irradiating the modules or ground currents.

The array consists of 16 DP&W top of pole mounts with 10 modules each, arranged 
in a square of 4 poles E-W and 4 rows N-S.  The poles are 13 feet center to 
center E-W and the N-S row spacing is about 50 feet.  The poles are 6 inch 
galvanized Technoposts, augured 5 - 7 feet into the firm ground, connected with 
a network of about 160 feet of bare #6 copper and at least 8 copper plated 
ground rods.  Altogether we have about 130 square feet of bare metal surface 
area connected and buried in the ground at and around the array.

The customer saw lightning strike just after dawn a few weeks ago a couple 
hundred feet to the southwest where it also destroyed two utility pole mount 
distribution transformers and ran along the utility wires 100 feet south of the 
array.  The inverters are 200 feet NW and suffered no damage.  The array and 
modules look totally fine, except some of the J-boxes are deformed from heat.  
Opening the J-boxes shows varying levels of damage to one or more diodes, from 
discoloration to being broken and cracked open.

The odd thing is the pattern of damage (we've tested all the modules 
individually for Voc and Isc).  Only modules in the south row of 4 poles are 
damaged, and the damage is concentrated on the modules closest to the ground; 
modules higher up in the air appear OK.  Also, damage is less frequent as you 
move east, away from the direction of the strike.

If it was caused by ground currents, why would the current want to go up the 
poles, why only the southern row of poles, and why damage more modules closer 
to the ground and not those at the top?  Is it possible a flash near the ground 
irradiated the modules causing a current spike and the southern row shielded 
the other rows from most of the flash?  Anyone have experience with this?


Jeff Irish, PE
President
Hudson Solar
13 Hook Road
Rhinebeck, NY 12572
T.845.876.3767x110
F.845.876.3912
j...@hudsonsolar.com<mailto:j...@hudsonsolar.com>
Solar Electric Systems
NYSERDA Eligible PV Installer
NABCEP Certified Solar PV Installer
NABCEP Certified PV Technical Sales
MailScanner has detected a possible fraud attempt from "applewebdata:" claiming 
to be 
HudsonSolar.com<applewebdata://B5F2562A-2B67-4161-84E4-42F12DC28720/www.hudsonsolar.com>
2011 NYSERDA Excellence in Quality Award | 2011 NYSEIA Award Winner | 2009 Best 
of the Hudson Valley | 2008 SunPower Dealer of the Year | EDC Business 
Excellence Award for Innovation





_______________________________________________

List sponsored by Home Power magazine



List Address: 
RE-wrenches@lists.re-wrenches.org<mailto:RE-wrenches@lists.re-wrenches.org>



Options & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org



List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org



List rules & etiquette:

www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>



Check out participant bios:

www.members.re-wrenches.org<http://www.members.re-wrenches.org>




--
This message has been scanned for viruses and
dangerous content by Hudson Valley Computer 
Services<http://www.hvcomputerservices.com/>, and is
believed to be clean.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to