Eric,
Without challenging any of Dan's calculations, I will add that the BP SX170 has proven to be prone to failures. You didn't indicate which model of BP170 you have. I think that the SX170s are the model that was the source of BP's conditional recall of modules that could cause roof fires - no, I'm not making this up, but neither is my memory sharp about this.

Here's the text of an email dated 10/10/07 from Phil Undercuffler, now at Outback, then at Conergy:
 
BP reports that these failures tend to manifest early in the product
life; modules that will have problems will generally fail in the first
few years of service.  Failure rates are reported as .02% of product
distributed in US, .03% in European market
 
Cause:  
The solder joint inside the low-profile potted J-box on MC connected 
modules is what is failing.  

Changes in solder formulation (due to the phase out of lead solder 
for environmental reasons) and move to heavier gauge wire made it
harder to make a good solder joint.  

Failure of the solder joint causes heating and arcing, which can in 
certain cases ignite the epoxy material surrounding the joint.   

BP's concern is the potential for the burning epoxy to ignite 
flammable materials in the close vicinity of the junction box.  

BP does not believe that standard roofing materials such as asphalt 
shingles, tile or metal roofs will be affected by this issue.  

A dealer can perform tests with a relatively inexpensive infrared 
thermometer or contact thermal probe.  It is best to measure the 
module from the front, while in operation.

Problem modules will show 10-20 C difference between the solder 
joint and the module field just before failure.  
 
 
For solder connection, gather the following info:
Measure VOC and ISC
Physical examination, looking for brown or black spots on
solder traces
Model number
Serial number

They are rated at +/- 9%, one of the worst specs around at that time. We used quite a few of them at that time and have replaced many of them under warranty, including one entire 40-module commercial array, identical to the one you described.

I would still encourage testing individual string outputs for Vmp and Imp under load, to look for significant variances. At worst, it gives you a baseline reading. Also, if you can, look for browned hot spots, visible beneath he glass in the area over where the leads leave the module back.
Allan

Allan Sindelar
al...@positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder and Chief Technology Officer
Positive Energy, Inc.
3209 Richards Lane (note new address)
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com



On 7/22/2012 10:56 AM, Exeltech wrote:
Eric,

I checked my magic spreadsheet for the BP SX170.

Using 800W/m^2 irradiance, and a presumed ambient of 37C (98F),
everything appears to be working within specified tolerances.  The
presumed conditions create exactly your measured Voc, which is
why I used them.  Other temperature and irradiance combinations
will also work...

The voltage delta you measured between Voc and Vmpp is within
BP's specifications.  No PV has a perfect "fill factor".  Fill factor is the
aspect that determines the shape of the V/I curve established when
Voc and Vmpp are plotted.  The BP you mentioned have a fill factor of
0.769, which is very typical of polycrystalline PV.  A perfect fill factor
would be 1.0 (Vmpp equal to Voc), which obviously doesn't happen.
Thus, all PV have an operating voltage at maximum power that's below
the open circuit voltage -- some more than others.


Measured:
375Voc
280V at inverter at mpp
14-15A (fluctuating) at mpp

Calculated:
375Voc
301V mpp
14.96A mpp

Assumed:
800 w/m^2
37C (98F) amb

4,503W array power under above conditions

280V measured at the inverter
14.5A

Presuming 301V is correct Vmpp, this equates to:
 
1.38 ohms total system R, and 290W loss

290W/4503W = 6.44%

6.44% total loss --higher than a 2.5-3% best-practices target, and likely
due to slightly oxidized and/or loose connections in the DC-side of the
system.  Could also be due to long conductor runs, slightly undersized
conductors for the amperage and length, or both.

As Jeff Quackenbush mentioned, Vmpp is slighly lower than one might
expect, but doesn't appear to rise to the level of something that would
yet be indicative of something wrong.


Dan




--- On Sat, 7/21/12, SunHarvest <e...@harvesthesun.com> wrote:

From: SunHarvest <e...@harvesthesun.com>
Subject: [RE-wrenches] Low power production at a winery: DC voltage drop upon SB6000 start-up
To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
Date: Saturday, July 21, 2012, 3:19 PM

Hello Wrenches,
 
I am helping a client troubleshoot a complaint about underproduction of his on-grid system installed about 6-8 years ago. At first I thought I might encounter the bad Kyocera KC120 issue but it turns out they have BP170's, 40 of them for an STC power rating of 6.8kW.
 
Ratings of the BP modules: PTC=150.7, Vmp=35.4, Voc=44.2, Imp=4.8, Isc=5
 
The system has four panels of ten modules wired in series for a nominal rating of about 350v, 4.8a per string.
 
At the DC disconnect (first accessible combiner) I measured: All strings right at about 375v(oc), 4.7a(mp). After the strings are combined, at the DC input of the SB6000 (with the AC power to the inverter OFF) I measured about 375V as expected. Once the AC power is connected, the SB6000 starts up, and MPP operation is initiated, the DC voltage drops to about 280V, and amps sit between 14 & 15A.  I didn't think the voltage was supposed to drop upon MPP tracking...especially this much. This voltage drop would account for the observed power loss between actual and rated production values. I'm going to check with SMA but I wanted to ask the experts here too, as someone may advise something like, "Oh yeah, BP modules have a similar defect as the Kyocera..."
 
My questions:
 
Is the DC voltage supposed to drop significantly in MPP mode on these inverters?
If not, does this indicate a bad inverter?

Anyone know of problems with BP modules manufactured around 2006-2008?
 
The Kyocera modules showed good volts and amps until a load was connected. Seems like a similar issue here.
 
Eric Stikes
SunHarvest Solar
A Sustainable Energy Group Partner
+1 (530) 798 - 3738
www.harvesthesun.com



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to