The funny thing about requiring a disconnect on both sides of the meter is that the meter is only energized from one source - the utility. And for that matter, 230.82 permits a meter to be on the supply side of a service disconnect (it sounds like you were proposing the meter would be on the load side of the PV System Disconnect). Anything having to do with the arrangement between a meter and a disconnect (or disconnects) is either a local amendment, utility requirement or an incentive program requirement. Couldn't you even have a meter with no disconnect (as far as the NEC is concerned)?
Isaac Opalinsky
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org