Hello Steve,
In my case, I tightened the voltage window to 110 lower, 125 upper
and the transfer delay to 30. This made no difference. I did not
confirm SETUP/FX/INPUT ...ac transfer control set to GEN.
On Jun 15, 2010, at 7:15 AM, Steve Higgins wrote:
William,
Check to make sure what Input you have selected… go to SETUP/FX/
INPUT… Verify that you have the Ac Transfer control set to Gen.
Make sure that you have adjusted the transfer delay cycles in the
right screen... ADV/FX/GEN under Transfer delay cycles… I would
set this to 0.
As Mick said.. Check the Lower limit on the AC Voltage… ADV/FX/
GEN… AC2 Gen Lower Limit I would adjust this up to 110-112?
What does he have the cool down timer set to?
I would suggest 5-10 minutes Look under… ADV/MATE/AGS/SETUP… I
would set this to at least 5-10 minutes just to let the genset cool
off before shutting off.
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-
boun...@lists.re-wrenches.org] On Behalf Of William Miller
Sent: Monday, June 14, 2010 10:32 PM
To: RE-wrenches
Subject: [RE-wrenches] Gen set problems
Wrenches:
I have a customer that has a problem with a new generator. He has
two VFX3648 inverters in Outback stacking. He acquired a new
generator, a Kohler 12RES, a reputable make and model. Below is a
description of the problem:
The 12RES seems to be operating OK except for one problem. At the
end of a charging cycle, when the gen automatically shuts down and
load goes back to the inverters, all lights, TVs, etc., flash, one
TV shuts off, and a GFI trips. This has happened every time. It
did not happen with the 15RES or the smaller back-up gen (which was
disconnected manually). With the 15RES the same GFI would
occasionally trip while the unit was charging and handling house
load, but never at the auto shutdown point. I replaced the GFI,
but it still trips. There are three GFIs in the house, but only
one--always the same--trips.
I suggested he adjust the AC2/Gen transfer delay to a lower
number. He reduced it to minimum and this did not resolve the
problem. I also had him verify that the AC source is selected as
generator, which it is.
Do you have any suggestions?
Thanks in advance,
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic
Communication Privacy Act, 18 U.S.C. sections 2510-2521, is
confidential, and may also be protected by attorney-client or other
privilege. If you believe that it has been sent to you in error,
please do not read it. If you are not the intended recipient,you
are hereby notified that any retention, dissemination,
distribution, or copying of this communication is strictly
prohibited. Please reply to the sender that you have received the
message in error, then delete it. Thank you.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org