William,
I am having the same problem with a newly installed 8.5RES with a
single VFX3648. The problem was somewhat corrected for a auto start
shutdown by setting the generator cool down to one minute. This
unloads the generator before the generator is shut down and
eliminates the nasty relay chatter in the inverter followed by a surge
(indicated by a flash in the lighting) . There is still however a
'hammering' in the step down transformer.
With a MAN-OFF there there is still a chatter and surge before the
inverter and generator say goodbye to each other.
I am planning on adding a contactor to disconnect the generator input
with the generator start relay unless another solution exists.
I am wondering if Kohler has changed something and the two no longer
get along? The next time that I go to the job site I am going to
check the shutdown of the generator with the OB system disconnected.
I am also going to try a second backup generator.
Thirsty Lake Solar
Jeff Wongstrom
NABCEP Certified Solar Installer
University of Montana College of Technology
Renewable Energy Instructor
406-219-1119
thirstylakesolar
energytechnology
On Jun 14, 2010, at 11:31 PM, William Miller wrote:
Wrenches:
I have a customer that has a problem with a new generator. He has
two VFX3648 inverters in Outback stacking. He acquired a new
generator, a Kohler 12RES, a reputable make and model. Below is a
description of the problem:
The 12RES seems to be operating OK except for one problem. At the
end of a charging cycle, when the gen automatically shuts down and
load goes back to the inverters, all lights, TVs, etc., flash, one
TV shuts off, and a GFI trips. This has happened every time. It
did not happen with the 15RES or the smaller back-up gen (which was
disconnected manually). With the 15RES the same GFI would
occasionally trip while the unit was charging and handling house
load, but never at the auto shutdown point. I replaced the GFI,
but it still trips. There are three GFIs in the house, but only
one--always the same--trips.
I suggested he adjust the AC2/Gen transfer delay to a lower
number. He reduced it to minimum and this did not resolve the
problem. I also had him verify that the AC source is selected as
generator, which it is.
Do you have any suggestions?
Thanks in advance,
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: will...@millersolar.com
http://millersolar.com
License No. C-10-773985
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-
wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org