Hi folks:
    (Eric, by 'directly to the utility grid' I do mean with a breaker)
   Jason and  Allen, I agree with what you are saying, in theory, but in 
practice, it is not always possible.  I am installing a generator in a couple 
of weeks for a customer with an existing 9 KW array.   The property's main 
service is located at a separate building from the house, loads, and solar.  
The main panel feeds 200 Amps to the main residence and 200 Amps to a barn 
building (300 ft away)  The barn building has the array at it, and also the 
well pump, which needs to be backed up by the generator.  This requires us to 
either dig a 300' trench or just leave the system in auto.  We will be 
utilizing a 200A Automatic Transfer Switch, but we will not be able to place 
the generator into Auto mode.  The customer understands the situation, and said 
that he would leave the genny in 'manual' start mode.  I feed good about the 
situation, will disable the auto-start system, and will provide competent 
labelling.

 Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Jason Szumlanski <ja...@fafcosolar.com>
To: re-wrenches@lists.re-wrenches.org
Sent: Mon, March 1, 2010 3:50:23 PM
Subject: Re: [RE-wrenches] Generators and Grid-tie Systems

This is déjà vu.

I would say that the only safe and "correct" way is to connect the PV inverter 
output on the line side of the transfer switch. If you are on the generator 
side of the xfer switch, you are asking for trouble. The only other choice 
would be to use a contactor to ensure PV disconnection when the grid is down - 
then you could tap the PV on the load side of the transfer switch. 

And to answer Eric's #1 question in the original post, you may not need to 
resize/replace the panel if you follow this approach. We go with a line side 
tap in this scenario unless there is a compelling reason to do otherwise.

Jason Szumlanski
Fafco Solar
http://fafcosolar.com

>>> Hi Eric:
    Did you notice my e-mail on this subject last week?  I was hoping that 
someone would have some new, more concrete information on this subject, but I 
guess the old story still applies.  Here is the basic run down.
    The inverters will likely see the generator as utility power, especially if 
it is a decent quality generator, with a clean wave form.  The inverters will 
connect to the generator and back-feed the power into the generator's 
alternator, causing heat and generator failure.  The solar will burn up the 
alternator.  I have heard that this has occurred before.
    The only way to prevent this is to connect the solar directly to the 
utility power (not through the >generator's backed-up emergency load center.)  
>    If you must connect the solar through the generator's emergency load 
> center, then the generator must >not be placed into "Auto," but must instead 
> be in "manual."  The customer must be clear that the solar >breakers must be 
> turned off before the generator is turned on.  This probably should include 
> signage >which makes this clear to the customer.

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


      
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to