In my earlier post, I was about to make the claim that we could avoid the metal conduit with the Enphase inverters, then I reread it and saw that it covered inverter output as well. It seems to me that the AC line is no more dangerous than any other AC branch circuit in the house, and should be treated as such. Ahh, but the wording....I guess we have to wait till 2011 because of a typo? Also, I'm not sure if PV is the best word choice. The AC output of the Enphase inverter could be considered to be PV by some AHJs. I think keep DC, and drop the mention of inverter output completely.

Ray

On Oct 26, 2008, at 10:36 PM, Kelly Keilwitz, Whidbey Sun & Wind wrote:

Hi Ray,
I'm curious to know why you think that metallic conduit is required for the inverter AC output. 690.31(E) specifically addresses DC source and output
circuits.

We have an AHJ who interprets the section the same as you and I've been working to turn him (as he's now responsible for training other inspectors on PV in our Region). Toward that goal I asked John Wiles for his input. He
said:

" The intent of 690.31(E) is to apply only to the always-energized DC
circuits and not to the ac output circuits from the inverter since they go
"dead" as soon as the circuit to the utility is opened at any point.
There was a typo in 690.31(E) in the 2008 NEC. The word "of" should have
been "to" in front of the word "inverter".  The typo occurred in the
original submission (by me) to the Code Making Panel. The typo was not
detected during the review process. The word "PV" modifies both "source"
and "output" .
The attached proposal is being submitted for the 2011 NEC that will make
corrections and expansions to 690.31(E)."

I'd be interested to know if other wrenches are being subject to the same
interpretation (i.e. inverter AC must be in metal).

-Kelly

Kelly Keilwitz, P.E.
Whidbey Sun & Wind, LLC
Renewable Energy Systems
NABCEP Certified PV Installer
987 Wanamaker Rd,
Coupeville, WA 98239
PH & FAX 360-678-7131
[EMAIL PROTECTED]
On 10/24/08 10:31 AM, "R. Walters" <[EMAIL PROTECTED]> wrote:


You run AC wiring right to the AC disconnect from the roof. You still have to comply with 690.31E, (steel conduit to the disconnect is required for both DC or inverter output to the first readily accessible disconnect)) but you only need a single AC disconnect. No combiner box, No accessible DC disconnect.


Ray Walters








_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


R. Walters
Solarray.com
NABCEP # 04170442       



_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to