On 13 Sep 2024 at 12:56, (-Phil-) via EV wrote:

> You shouldn't be pulling more than 20A on #12 anyway 

For sure, and that only for short periods. Continuous loads shouldn't exceed 
16 amps (80% of maximum).

Not to be too preachy here, but if you really have AWG 12, your wiring is 
pretty seriously undersized - dangerously so, unless it's protected with a 
fuse or breaker at 20a, which doesn't seem to be the case.  

For 40 amp protection, AWG 8 copper or AWG 6 aluminum would be the minimum.

However, the NEC recommends (but I don't think requires) no more than 5% 
total voltage drop from main panel to point of use.  At 500', AWG 4 copper 
will get you 6% voltage drop, and AWG 1 aluminum 5%.  