Hi Robert,
I am afraid that some of your assumptions are wrong, so the wrong
conclusion follows.

You claim that the installation is expensive because of the large size
of the installation, but you forget that outdoor NEMA 5-20 outlets are
standard and cheap, so while the (underground) wiring to the outlets can
be costly, as long as it is done in standard conduit and outlets are
aggregated in a smart way to a limited number of conduits, the total
installation is neither complicated nor very expensive, especially when
done during construction of the parking. Look at how public parking has
street lights put in, distributed throughout the lot? Adding vehicle
charging will certainly increases the amount of wiring but if done in a
smart way, not much more digging or conduit required. Just fatter cables
to supply more power and more branching out at the end.

You claim that there is a maintenance issue because of a large number of
EVSE, I thought the idea was that there are no EVSE needed, just NEMA
outlets. Those do not fail very often and don't need maintenance.

Puddles a problem? How about GFCI outlets that are already required in
new buildings? And how do you think that the northern states that have
an outlet in every parking spot for block heaters have been managing
this "danger"?
For many years I plugged into such an outlet, whether it was raining or
the sun was shining and I never wondered if it would be a problem. I
knew the GFCI would detect any problem.

System security: What did you have in mind? Someone hacking the 110V
outlet?
If stealing power is an issue then the building manager can put the
parking lot outlets on a timer to turn off after hours.

You say that the system will have a low utilization rate because the EV
needs to be parked (charging) for a long time. This indicates a high
utilization rate.

The cost of the system is not high if you compare to the cost to the
company of the employee salaries. Playing musical chairs with EVs in the
parking lot, causing each employee to lose up to half hour of work time
might cost the company in the order of $100 per occurrence, so $20,000
per employee per year. The cost of installing a hundred NEMA outlets for
200 employees pales in comparison and the convenience of not needing to
search for a charger, but simply drop the car in a slot and plug in for
the day are a much better proposition than the hassle of waiting or
running out to move the car in time or even a valet service to get all
participating EVs charged.

There probably are scenarios possible where a limited number of high
priced EVSE make sense and I fully support to have a few high power EVSE
available for the "Oh crap" moments where you need to leave ASAP but
have not enough range, so you gladly pay a couple bucks to fill up in
minutes instead of hours. But the regular commute traffic can perfectly
be done with 110 outlets, as I know from experience.

Hope this clarifies the discussion.

Cor van de Water 
Chief Scientist 
Proxim Wireless 
  
office +1 408 383 7626                    Skype: cor_van_de_water 
XoIP   +31 87 784 1130                    private: cvandewater.info 

http://www.proxim.com

This email message (including any attachments) contains confidential and
proprietary information of Proxim Wireless Corporation.  If you received
this message in error, please delete it and notify the sender.  Any
unauthorized use, disclosure, distribution, or copying of any part of
this message is prohibited.


-----Original Message-----
From: EV [mailto:[email protected]] On Behalf Of ROBERT via EV
Sent: Sunday, November 06, 2016 7:15 PM
To: Lee Hart; Electric Vehicle Discussion List
Subject: Re: [EVDL] Cheap L2 charging in parking places: Bolt EV'sIn
Production

Lee, I was making the following points in my e-mail concerning the
installation of a large number of EVSEs in a parking area:


(1) The installation will be very expensive because of the size of the
required electrical distribution system

(2) Maintenance will be expensive because of the large number of EVSEs
and equipment failure rates

(3) The system will have a low utilization rate because vehicle will be
parked for an extended periods

(4) System security is low because of scammers and no local oversight

(5) Not a safe system because of a possible pool of water or vandalism.

(6) The cost of an EVSE is small relative to the cost of the system;
therefore, a lower cost intelligent outlet will have a minor impact on
the total system cost.


Due to the above points, the installation of a large number of EVSEs in
a parking area (1) is not an efficient use of equipment, (2) has low
system security, (3) unsafe system and (4) is not a good use of capital.


My suggestion to solve the problem was for everyone to charge at home
with a NEMA type outlet or use an induction type system in a parking
area.


An induction type system reduces the installation cost because of a
reduction in the size of the electrical distribution system.  With an
induction coupled system, the main source can sense the presence of a
vehicle or if a vehicle requires power; therefore, the main source can
be sized to the utilization rate.  The main source can alternate between
vehicles.  This cannot be done with an EVSE system.  The NEC requires
that the service required for each EVSE be sized at full load.  See Perl
Hartman e-mail describing a 100 plug L2 system.  It required 2000A at
120VAC.  With a 20% utilization rate, the induction system would only
require 400A at 120VAC.  Maintenance cost would be lower because the
system consist of a main power source, distribution panel, and numerous
coils of wire.  The system is safer because it is not effected by water
and is secure from vandalism.


Other technical points:

An X10 system (PowerLine Transmission) will not work in an industrial or
commercial environment because of signal attenuation, electrical noise,
transmission across transformers, and low data transmission rate.  RF is
not reliable in a structure with high levels of electrical noise or a
lot of rebar (steel) and concrete.  Cell phones and radios do not work
reliably in underground or high rise parking garages or some houses.  In
my house, I cannot use a wireless modem.  My house has to much rebar,
concrete, and earth.


I looked at the nameplate on the Magne Charger that I have in my
workshop.  It showed: Charge Port CP7100, 475VAC Peak, 22A AC Max, 400
Hz, 6.5 KW Max Output Power, Manf Date July 1996.  Also, it showed the
manufacturer as Delso Electronics Power Control Systems.  This is the
unit that is installed in the car.  I could not find the nameplate data
on the pedestal unit with the paddle.  If you have any electrical
schematics or other info on these units, I would be interested.  Thanks
Bob Hensley.


________________________________
From: EV <[email protected]> on behalf of Lee Hart via EV
<[email protected]>
Sent: Sunday, November 6, 2016 9:59 AM
To: Electric Vehicle Discussion List
Subject: Re: [EVDL] Cheap L2 charging in parking places: Bolt EV's In
Production

ROBERT via EV wrote:
> An EVSE requires an AC cable and data cable. An intelligent outlet
> would still require the same two cables. In addition, a specialty
> intelligent outlet would cost $100 - $200 (guesstimate).

Not really. An intelligent outlet could do the same, and use RF, or
carrier current signalling to communicate with the EV.

For example, the GM EV1 Magnechargers used RF signals for
authentication. Remember, they had *no* wires between the vehicle and
EVSE.

The common X10 system is used to remotely control all sorts of AC loads.
Special outlets have a circuit that can send and receive data over the
existing AC power line wiring, and can switch the AC on or off. These
outlets are mass-produced and sell for only $20 or so each.

> However, the high cost is the installation cost and maintenance cost.

People forget that large areas of the nation have already had a charging
infrastructure for a very long time. It's been there to plug in ICE
block heaters, Christmas lights, run electric lawnmowers, etc.

Outdoor AC outlets have been required by the NEC (National Electric Code
for decades. In the states where I've lived (Michigan, New York, and
Minnesota, just about every home, apartment, and business has these
standard 120vac 15a convenience outlets already installed and freely
available for use.

> High installation and maintenance cost are a problem with developing
> an EV charging infrastructure. The answer is to charge at home with a
> NEMA outlet or install induction charging stations.

That's true, if they insist on something new, proprietary, and
incompatible with existing systems. Unfortunately, these become the
*requirements* when someone wants to create a new monopoly to get rich.

> However, for induction charging to work efficiently, you need higher
> frequency chargers.  Remember the EV1 induction charging paddle. The
> system operated at 400 HZ.

The EV1 Magnecharger worked at a much high frequency (around 50 KHz).
The higher frequency actually *hurt* efficiency, but was necessary to
make the paddle small and light.

We've had 60 Hz induction charging setups for 50%+ years. For example,
Inductran has made them for charging in-plant EVs. Half of a
conventional 60 Hz transformer is in the floor, and the other half in
the vehicle. Drive over it, and turn it on. The two halves of the
transformer magnetically link, to charge safely and efficiently.

We don't really need expensive high-tech solutions for charging. It's
fundamentally no different than plugging in any other appliance, and
people have been doing that for 100 years.

--
Buy thneeds! It's what everyone needs! Get em' now 'fore they're gone!
Which they'll be, before long! -- "The Lorax" by Dr. Seuss
--
(The reasonable man adapts himself to the world. The unreasonable man
persists in trying to adapt the world to himself. Therefore all
"The Lorax" by Dr. Seuss
--
Lee Hart, 814 8th Ave N, Sartell MN 56377,
www.sunrise-ev.com<http://www.sunrise-ev.com>
The Sunrise EV2 Project<http://www.sunrise-ev.com/>
www.sunrise-ev.com
The Sunrise EV2 Project Homepage. Welcome! We are a group of dedicated
electric vehicle enthusiasts whose goal is to create an affordable, high
performance electric ...


_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
EV -- Electric Vehicle Discussion List - lists.evdl.org
...<http://lists.evdl.org/listinfo.cgi/ev-evdl.org>
lists.evdl.org
The Electric Vehicle Discussion List is a forum for discussing the
current state of the art and future direction of electric vehicles
(EVs). We define an EV as a ...


Read EVAngel's EV News at http://evdl.org/evln/
EVDL EV News Archive - Electric Vehicle Discussion
List<http://evdl.org/evln/>
evdl.org
EVLN - EV News Archive Edited by Bruce {EVangel} Parmenter: EVLN: home |
help | archive | news | privacy policy | terms of service


Please discuss EV drag racing at NEDRA
(http://groups.yahoo.com/group/NEDRA)
[https://s1.yimg.com/dh/ap/default/130909/y_200_a.png]<http://groups.yah
oo.com/group/NEDRA>

Yahoo! Groups<http://groups.yahoo.com/group/NEDRA>
groups.yahoo.com
/



-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20161107/dfd6
013e/attachment.htm>
_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
Read EVAngel's EV News at http://evdl.org/evln/
Please discuss EV drag racing at NEDRA
(http://groups.yahoo.com/group/NEDRA)

_______________________________________________
UNSUBSCRIBE: http://www.evdl.org/help/index.html#usub
http://lists.evdl.org/listinfo.cgi/ev-evdl.org
Read EVAngel's EV News at http://evdl.org/evln/
Please discuss EV drag racing at NEDRA (http://groups.yahoo.com/group/NEDRA)

Reply via email to