My turn to ask a question to the group of experts.

 

Reference:

IEC 61000-2-4:2024

Electromagnetic compatibility (EMC) - Part 2-4: Environment - Compatibility 
levels in power distribution systems in industrial locations for low-frequency 
conducted disturbances

 

My client would like to know if standard IEC 61000-2-4 is applicable to an 
inverter that is intended for permanent installation in a motor vehicle.  The 
inverter has no connection to a.c. mains and does not have an a.c. input power 
port.  It’s merely a 24Vdc to 230Vac/50Hz inverter.

 

I think this IEC standard is clearly out of scope for this class of equipment, 
but if client’s customer insists (a big automotive manufacturer) I’d like to be 
able craft a technical justification to waive application of the standard.

 

The standard appears only to address conducted disturbances which may be 
present on non-public (industrial) a.c. power networks and the EMC immunity of 
equipment connected to those networks.

 

Thank you,

 

 

Ralph

 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
[email protected]

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to