On 8/26/2015 2:33 PM, Paul Koning wrote:
> 
>> On Aug 26, 2015, at 3:16 PM, Jay Jaeger <cu...@charter.net> wrote:
>>
>> On 8/26/2015 8:19 AM, Paul Koning wrote:
>>>
>>> I heard of this sort of thing happening to the DEC building at Marlboro.  
>>> Supposedly it had two mains entrances, served from different power lines 
>>> (and different companies?  Seems odd).  One of the machine rooms had feeds 
>>> from both ends, and one particular system was fed from both.  What happened 
>>> is that the "grounds" were offset enough, and with enough of a current 
>>> supply, that the ground strap that's supposed to connect the row of RP06 
>>> drives melted.
>>>
>>> This sort of thing is a major electric code violation: you can certainly 
>>> have multiple services, but all the grounds are required to be connected by 
>>> substantial wire; you're not allowed to stick ground rods in at multiple 
>>> places and leave it at that.  (The same goes for lightning rods.)
>>>
>>>     paul
>>>
>>
>> Quite possibly two different phases, and if so, the would be 90 degrees
>> out of phase with each other.
> 
> 90?  Three phase power is 120 degrees apart, center-tapped "two phase" home 
> power is 180 degrees, but I don't know of any power company service that 
> produces 90 degree shifts.
> 

Yes, of course:  120 degrees.  D'oh.

> In any case, RP06s use three phase power.  The issue wasn't the power in this 
> particular story, but rather the ground wire (the green "protective ground" 
> that isn't supposed to carry current at all under normal operation).
> 
>       paul
> 
> 

I understand. Different shocks for different folks.  ;)

JRJ