On 8/26/2015 8:19 AM, Paul Koning wrote:
> 
> I heard of this sort of thing happening to the DEC building at Marlboro.  
> Supposedly it had two mains entrances, served from different power lines (and 
> different companies?  Seems odd).  One of the machine rooms had feeds from 
> both ends, and one particular system was fed from both.  What happened is 
> that the "grounds" were offset enough, and with enough of a current supply, 
> that the ground strap that's supposed to connect the row of RP06 drives 
> melted.
> 
> This sort of thing is a major electric code violation: you can certainly have 
> multiple services, but all the grounds are required to be connected by 
> substantial wire; you're not allowed to stick ground rods in at multiple 
> places and leave it at that.  (The same goes for lightning rods.)
> 
>       paul
> 

Quite possibly two different phases, and if so, the would be 90 degrees
out of phase with each other.

JRJ