NEC is designed for electrical safety.  It's based on the size of the
conductor necessary to permit a breaker to trip when you have a ground
fault.

R56 is designed to improve survivability of  lightning strike or other EMP
event.  The wires are sized large enough to ensure a low impedance
(resistance) path interconnecting all parts of the grounding system.  These
oversized conductors minimize voltage differences when carrying the
significant current caused by a strike.  These will generally be larger
than the NEC sizes.

And, in the case of vendor specs, it's hard to know the motivation.

On Tue, Jan 7, 2025, 9:15 AM Adam Moffett <dmmoff...@gmail.com> wrote:

> I found some code references saying that an equipment ground wire should
> be either equal in size to the power conductor to the equipment or based on
> the amperage of the circuit protection device.  For example, a device on a
> 20A breaker would use the larger of 12ga or the size of the power conductor
> to the device.
>
> But then you have things like R56 calling for nothing smaller than 6 gauge.
>
> And then I have manufacturer installation guides which may go a step
> further and call for 4 gauge or 2 gauge.
>
> So why the apparent overkill?  Is it for mechanical robustness?
> Performance even if connections are corroded or incorrectly torqued?  I'm
> ok with all of that, I'm just wondering if they just want a big safety
> margin or if there's some electrical reason why I'd need a 2 gauge ground
> for a piece of equipment with 70A @ -48VDC breakers.
>
> -Adam
>
> --
> AF mailing list