[X]

Looking at the actual text of the code I see why there was some confusion in my 
Google results.  Yeah you size the equipment ground based on the ampacity of 
the protection device, but if you install larger than necessary power 
conductors you have to proportionately upsize the ground.

I’ve got an installation guide from Nokia calling for a 4 gauge ground and that 
didn’t make sense to me, but I think I got to the bottom of it.   They call for 
2-gauge power conductors, which would be stupid overkill for 70A unless you 
consider an installation in a CO where you might connect to a power plant 40ft 
across the room.  Then you DO need 2 gauge power wires, and if you upsized the 
power cable that much then you have to upsize the ground.  So if they have to 
give an installer one number they’re giving them a safe number.

With a 4ft power run to a rectifier in the same rack I think I could drop all 
of those power and ground conductors to 6-ga rather than fight a bundle of 2-ga 
anacondas through the rack.

Get Outlook for iOS<https://aka.ms/o0ukef>
________________________________
From: AF <af-boun...@af.afmug.com> on behalf of ch...@go-mtc.com 
<ch...@go-mtc.com>
Sent: Tuesday, January 7, 2025 12:08:34 PM
To: AnimalFarm Microwave Users Group <af@af.afmug.com>
Subject: Re: [AFMUG] Equipment Ground Wire Sizes

Depends on if you are grounding for safety and circuit breaker blowing, like 
for a receptacle, or grounding for surges etc.  They keep trying to convince 
the world that a small surge suppressor needs a #6 wire, but that is almost 
impossible.  #10 works well for surge suppressors.

As far as the NEC is concerned, you can go smaller than the current carrying 
conductors for the grounds.  120.122 has the rules but for example a 60 amp 
circuit can use a #10 wire.  It has to do with what the circuit breaker needs 
in order to properly interrupt the current during a fault.  For 15 and 20 amp 
circuits you normally would use a #14 and #12 ground respectively.

From: Adam Moffett
Sent: Tuesday, January 7, 2025 9:14 AM
To: AnimalFarm Microwave Users Group
Subject: [AFMUG] Equipment Ground Wire Sizes

I found some code references saying that an equipment ground wire should be 
either equal in size to the power conductor to the equipment or based on the 
amperage of the circuit protection device.  For example, a device on a 20A 
breaker would use the larger of 12ga or the size of the power conductor to the 
device.

But then you have things like R56 calling for nothing smaller than 6 gauge.

And then I have manufacturer installation guides which may go a step further 
and call for 4 gauge or 2 gauge.

So why the apparent overkill?  Is it for mechanical robustness?  Performance 
even if connections are corroded or incorrectly torqued?  I'm ok with all of 
that, I'm just wondering if they just want a big safety margin or if there's 
some electrical reason why I'd need a 2 gauge ground for a piece of equipment 
with 70A @ -48VDC breakers.