Right, the problem with rackmount IMO is depth.  You need a deeper cabinet and for some reason that drives cost up.  Does the Packetflux PDU accept -48 now? Used to be it didn't and that was a show stopper for me.  Actually I ended up connecting the single relay on the Site Monitor to the reset contact on the Traco BCM.....I figured we could add the PDU later if they made a -48 version and for the short term we'll just reboot the whole site if we need to reboot anything. I did that for 25 sites, 4 years ago and haven't really looked back at adding the PDU.  So that's one way to keep it simple/cheap.

-Adam


On 6/21/2019 10:35 AM, Josh Baird wrote:
For this we use a PacketFlux SiteMonitor.  The contacts on the Traco BCM/BCMU connect to the "switch" input on the SiteMonitor to let us know when the site loses AC power. When we require switched loads, we add a PacketFlux 5Channel PDU which can be monitored/controlled remotely via the SiteMonitor.

For 1U solutions, the ICT that Adam linked to looks super nice.  I have been trying to find an excuse to buy/try one. We don't have rack space at most of our sites though (except for larger sites), so the DIN rail stuff makes more sense most of the time.

On Fri, Jun 21, 2019 at 10:25 AM Adam Moffett <dmmoff...@gmail.com <mailto:dmmoff...@gmail.com>> wrote:

    When you do a setup with the industrial Meanwell, Traco, etc stuff
    one thing to keep in mind is monitoring.  With that class of
    equipment you'll have dry contacts and you'll need something to
    monitor those for alarms.  You'll probably want a current shunt
    and then either a set of Packetflux modules or something like a
    Tycon TPDIN-Monitor-WEB2.

    Then think about remote control and power distribution.  If you
    don't want/need to reboot individual devices then distribution can
    just be a set of terminal blocks.  If you DO want/need to reboot
    individual devices then you need some kind of PDU with either
    relay contacts or an ethernet connection.

    So I'm going to point in a completely different direction now:
    http://www.ict-power.com/products/modular-power-series/
    or
    
https://www.vertiv.com/globalassets/products/critical-power/dc-power-systems/netsure-2100-a31-s1--ds-en-asia.pdf

    Either the Vertiv or ICT device linked above is a single 1RU
    device with rectifier, battery controller, network interface, and
    PDU with remotely flippable circuit breakers.  I have one of the
    ICT MPS units and the system is dead simple.  I think it's around
    $1500-1800 for that. That's probably double what you'd spend for
    an equivalent set of features with Traco or Meanwell combined with
    Packetflux modules.  However, you gain space efficiency, simpler
    design, simpler to set up, and simpler to use for you and your
    technicians.  And I'm pretty sure the ICT and Vertiv units both
    have relay contacts if you do need to monitor things like door
    sensors and such.

    The Alpha Cordex that Josh Baird linked to earlier does some of
    that, but doesn't include a PDU and it's 2RU. I'd looked real hard
    at Alpha, but it's a little more complicated to use, and by the
    time you add some kind of PDU you're using way more space than you
    would with ICT MPS or Vertiv NS2100.

    Don't take my word for it.  Try doing Site Monitors and industrial
    power supplies first.  If you're happy with that method then you
    will save money doing it.  I didn't go this other direction until
    I had to explain to a new technician how to use the Site Monitor
    and realized that there's no way to make it simple enough for a
    low level goon.

    Oh...and if remote monitoring and control aren't important for
    your case, then definitely do Meanwell or Traco. Way cheaper,
    smaller, and simpler.  It's when you start adding features that
    you encounter the complexity and size issue I'm talking about.

    -Adam


    On 6/20/2019 3:58 PM, Josh Baird wrote:
    Our typical setup medium sized sites is:

    Traco TSP-360-148 (360W @ 48V)
    Traco TSP-BCM48A (we usually put a string of 4 12-33ah 12V
    batteries on these)

    For very small sites, where we only need (or can fit) 1 12V
    battery, but still require 48VDC, we do:

    Meanwell SDR-240-48
    Traco TSP-BCMU (good for ~220W, can output either 24VDC or 48VDC
    with a single 12VDC battery.. we usually put a single 18-33ah
    battery on these)

    Voltage drop obviously depends on length of the run, but you
    should be able to easily calculate that. We usually adjust our
    PSU's (at the bottom) to ~54VDC and we typically see ~49-51VDC at
    the top.  Yes, you can tweak the output of both the Meanwell and
    the Traco to compensate for voltage drop if needed.

    We use a Shireen hybrid fiber cable which has a 12AWG pair for
    DC.  We use these up to 200ft or so.

    On Thu, Jun 20, 2019 at 3:47 PM Sterling Jacobson
    <sterl...@avative.net <mailto:sterl...@avative.net>> wrote:

        So what’s the Traco parts list for that?

        I don’t do this stuff normally, so excited to get started and
        try it out.

        If I’m pushing 48v up top to a roof, what’s the voltage drop?

        I assume these DC units can somehow be tweaked so that output
        can accommodate for voltage drop.

        What size wire is everyone using typically for this, usually
        30-100 ft max length?

        I’m assuming it’s something like 10 AWG? At 48v and 5A and
        50’ is maybe 47.5v at the end?

        So I would push 49 or 50v just to be safe?

        *From:* AF <af-boun...@af.afmug.com
        <mailto:af-boun...@af.afmug.com>> *On Behalf Of * Josh Baird
        *Sent:* Wednesday, June 19, 2019 8:19 AM
        *To:* AnimalFarm Microwave Users Group <af@af.afmug.com
        <mailto:af@af.afmug.com>>
        *Subject:* Re: [AFMUG] UPS and DC to DC conversion

        FWIW - we have lots of EdgePoint S16's that are powered by
        Traco BCM/TSP combos @ ~54V with no issues.

        I agree with others - your battery plant should be 48VDC.

        On Wed, Jun 19, 2019 at 10:15 AM Sterling Jacobson
        <sterl...@avative.net <mailto:sterl...@avative.net>> wrote:

            Yeah, I’ll probably just use 48v battery array in series
            and float higher.

            That particular device can do 48v, it just may shut down
            POE if it gets lower than 48v.

            *From:* AF <af-boun...@af.afmug.com
            <mailto:af-boun...@af.afmug.com>> *On Behalf Of
            *ch...@wbmfg.com <mailto:ch...@wbmfg.com>
            *Sent:* Wednesday, June 19, 2019 8:11 AM
            *To:* AnimalFarm Microwave Users Group <af@af.afmug.com
            <mailto:af@af.afmug.com>>
            *Subject:* Re: [AFMUG] UPS and DC to DC conversion

            Why not run your system at 54 volts?  If the radio freaks
            out above 54, just set it at 54 and you should be fine. 
            Battery strings don’t exceed the float voltage of the
            rectifier.  If you are worried about it float at 53.75
            volts.

            *From:*Sterling Jacobson

            *Sent:*Tuesday, June 18, 2019 11:19 PM

            *To:*AnimalFarm Microwave Users Group

            *Subject:*Re: [AFMUG] UPS and DC to DC conversion

            Having a hard time figuring out the exact part/price for
            something like this.

            Which Meanwell part would take 48v and make it 50v or 54v 5A?

            *From:* AF <af-boun...@af.afmug.com
            <mailto:af-boun...@af.afmug.com>> *On Behalf Of *Adam Moffett
            *Sent:* Tuesday, June 18, 2019 10:21 PM
            *To:* af@af.afmug.com <mailto:af@af.afmug.com>
            *Subject:* Re: [AFMUG] UPS and DC to DC conversion

            That's weird to me.  Any telecom equipment made for 48v I
            would have assumed they intended it to be used with a
            rectifier, and consequently I would assume it'd be ok up
            to at least 56v continuous; and maybe more like 60-70v
            for a short duration.  But yeah, DC-DC converter is the fix.

            On 6/18/2019 11:36 PM, Sean Heskett wrote:

                You need to use a DC-DC converter for sensitive
                equipment like that.  Meanwell has a good selection.

                On Tue, Jun 18, 2019 at 8:12 PM Sterling Jacobson
                <sterl...@avative.net <mailto:sterl...@avative.net>>
                wrote:

                    Apparently the UBNT EP-S16 freaks out if it goes
                    above 54v.

                    Is there any way to assure it doesn’t
                    float/charge above 54v, or maybe even just 50v?

                    *From:* AF <af-boun...@af.afmug.com
                    <mailto:af-boun...@af.afmug.com>> *On Behalf Of
                    *TJ Trout
                    *Sent:* Tuesday, June 18, 2019 7:26 PM
                    *To:* AnimalFarm Microwave Users Group
                    <af@af.afmug.com <mailto:af@af.afmug.com>>
                    *Subject:* Re: [AFMUG] UPS and DC to DC conversion

                    contact talley or tessco for a price, don't trust
                    what you see on google, it's like 50% less

                    On Tue, Jun 18, 2019 at 6:25 PM TJ Trout
                    <t...@voltbb.com <mailto:t...@voltbb.com>> wrote:

                        all 48v systems for battery power will float
                        at 54v, it's also adjustable via the battery
                        chemistry

                        On Tue, Jun 18, 2019 at 3:33 PM Sterling
                        Jacobson <sterl...@avative.net
                        <mailto:sterl...@avative.net>> wrote:

                            Ok, cool.

                            So can the 7bc2 be adjusted slightly to
                            output 50v instead of just 48v?

                            There will be some loss going 100’  or
                            so, right?

                            *From:* AF <af-boun...@af.afmug.com
                            <mailto:af-boun...@af.afmug.com>> *On
                            Behalf Of *TJ Trout
                            *Sent:* Tuesday, June 18, 2019 4:23 PM
                            *To:* AnimalFarm Microwave Users Group
                            <af@af.afmug.com <mailto:af@af.afmug.com>>
                            *Subject:* Re: [AFMUG] UPS and DC to DC
                            conversion

                            12-54v is inefficient, if you want 200ah
                            of battery use 4x50ah batteries for a 48v
                            string

                            ICT24048-7BC2 360W 54v AC-DC + LVD + Charger
                            ICT-TMP - Temp sensor for charge
                            compensation if batt's outside
                            ICT-WMB - Wall mount bracket
                            SITE Monitor - Voltage monitoring

                            Or

                            Alternativly;

                            48v din mount PSU
                            48v 'dc ups' to charge batt's and provide LVD
                            OR
                            48v din 'dc ups' with integrated psu +
                            lvd + charger (i.e. DIN-UPS 48-5 cheaper
                            options available)

                            On Tue, Jun 18, 2019 at 2:50 PM Sterling
                            Jacobson <sterl...@avative.net
                            <mailto:sterl...@avative.net>> wrote:

                                I’m trying to put a “box” system
                                together for our house POP sites and
                                need help with the DIN stuff and UPS.

                                Can you guys give me an idea or
                                example of the following?

                                I want to take standard AC 15A in
                                from a breaker outside the box.

                                And using maybe one or two 12v 105AH
                                AGM batteries, supply 50v 6A up the
                                side of the house.

                                I have never ordered DIN parts like
                                this, guess I don’t have to use DIN,
                                but would be nice.

                                Having a problem finding a DC to DC
                                converter that takes 12v and
                                upconverts to 50v 5-6A.

                                Is this the cost effective method?
                                Something like this:

                                Monitoring Sitemonitor Base Unit II
                                SMON Base II 1.00 $100.00 $100.00

                                UPS Monitor Sitemonitor Int
                                MorningStar MeterBus  SMON
                                MorningStar         1.00       
                                $60.00                 $60.00

                                UPS Charge MorningStar Sunsaver Dual
                                1.00 $165.00 $165.00

                                Battery AGM Deep Cycle 105AH NPP
                                FT12-105AH 2.00 $225.00 $450.00

                                DIN Parts like DC fuse/breakers and
                                trunk stuff 1.00 $100.00 $100.00

                                DC 12v to 50v 5A 1.00 $150.00 $150.00

-- AF mailing list
                                AF@af.afmug.com <mailto:AF@af.afmug.com>
                                
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- AF mailing list
                            AF@af.afmug.com <mailto:AF@af.afmug.com>
                            http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- AF mailing list
                    AF@af.afmug.com <mailto:AF@af.afmug.com>
                    http://af.afmug.com/mailman/listinfo/af_af.afmug.com

            
------------------------------------------------------------------------

-- AF mailing list
            AF@af.afmug.com <mailto:AF@af.afmug.com>
            http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- AF mailing list
            AF@af.afmug.com <mailto:AF@af.afmug.com>
            http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- AF mailing list
        AF@af.afmug.com <mailto:AF@af.afmug.com>
        http://af.afmug.com/mailman/listinfo/af_af.afmug.com



-- AF mailing list
    AF@af.afmug.com <mailto:AF@af.afmug.com>
    http://af.afmug.com/mailman/listinfo/af_af.afmug.com



-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to