We use a number of the Altech CBI485A power supplies for this application - 
48VDC 5A UPS for external batteries.   It has the same monitoring drawback as 
the other solutions - just dry contacts so we end up adding packetflux gear to 
monitor it.   It works fine but a true rectifier shelf is a far better answer.

Mark

> On Jun 21, 2019, at 10:35 AM, Josh Baird <joshba...@gmail.com> wrote:
> 
> For this we use a PacketFlux SiteMonitor.  The contacts on the Traco BCM/BCMU 
> connect to the "switch" input on the SiteMonitor to let us know when the site 
> loses AC power.  When we require switched loads, we add a PacketFlux 5Channel 
> PDU which can be monitored/controlled remotely via the SiteMonitor.
> 
> For 1U solutions, the ICT that Adam linked to looks super nice.  I have been 
> trying to find an excuse to buy/try one.  We don't have rack space at most of 
> our sites though (except for larger sites), so the DIN rail stuff makes more 
> sense most of the time.
> 
> On Fri, Jun 21, 2019 at 10:25 AM Adam Moffett <dmmoff...@gmail.com 
> <mailto:dmmoff...@gmail.com>> wrote:
> When you do a setup with the industrial Meanwell, Traco, etc stuff one thing 
> to keep in mind is monitoring.  With that class of equipment you'll have dry 
> contacts and you'll need something to monitor those for alarms.  You'll 
> probably want a current shunt and then either a set of Packetflux modules or 
> something like a Tycon TPDIN-Monitor-WEB2.
> 
> Then think about remote control and power distribution.  If you don't 
> want/need to reboot individual devices then distribution can just be a set of 
> terminal blocks.  If you DO want/need to reboot individual devices then you 
> need some kind of PDU with either relay contacts or an ethernet connection.
> 
> So I'm going to point in a completely different direction now:
> http://www.ict-power.com/products/modular-power-series/ 
> <http://www.ict-power.com/products/modular-power-series/>
> or
> https://www.vertiv.com/globalassets/products/critical-power/dc-power-systems/netsure-2100-a31-s1--ds-en-asia.pdf
>  
> <https://www.vertiv.com/globalassets/products/critical-power/dc-power-systems/netsure-2100-a31-s1--ds-en-asia.pdf>
> 
> Either the Vertiv or ICT device linked above is a single 1RU device with 
> rectifier, battery controller, network interface, and PDU with remotely 
> flippable circuit breakers.  I have one of the ICT MPS units and the system 
> is dead simple.  I think it's around $1500-1800 for that.  That's probably 
> double what you'd spend for an equivalent set of features with Traco or 
> Meanwell combined with Packetflux modules.  However, you gain space 
> efficiency, simpler design, simpler to set up, and simpler to use for you and 
> your technicians.  And I'm pretty sure the ICT and Vertiv units both have 
> relay contacts if you do need to monitor things like door sensors and such.
> 
> The Alpha Cordex that Josh Baird linked to earlier does some of that, but 
> doesn't include a PDU and it's 2RU. I'd looked real hard at Alpha, but it's a 
> little more complicated to use, and by the time you add some kind of PDU 
> you're using way more space than you would with ICT MPS or Vertiv NS2100.
> 
> Don't take my word for it.  Try doing Site Monitors and industrial power 
> supplies first.  If you're happy with that method then you will save money 
> doing it.  I didn't go this other direction until I had to explain to a new 
> technician how to use the Site Monitor and realized that there's no way to 
> make it simple enough for a low level goon.
> 
> Oh...and if remote monitoring and control aren't important for your case, 
> then definitely do Meanwell or Traco. Way cheaper, smaller, and simpler.  
> It's when you start adding features that you encounter the complexity and 
> size issue I'm talking about.
> 
> -Adam
> 
> 
> On 6/20/2019 3:58 PM, Josh Baird wrote:
>> Our typical setup medium sized sites is:
>> 
>> Traco TSP-360-148 (360W @ 48V)
>> Traco TSP-BCM48A (we usually put a string of 4 12-33ah 12V batteries on 
>> these)
>> 
>> For very small sites, where we only need (or can fit) 1 12V battery, but 
>> still require 48VDC, we do:
>> 
>> Meanwell SDR-240-48
>> Traco TSP-BCMU (good for ~220W, can output either 24VDC or 48VDC with a 
>> single 12VDC battery.. we usually put a single 18-33ah battery on these)
>> 
>> Voltage drop obviously depends on length of the run, but you should be able 
>> to easily calculate that.  We usually adjust our PSU's (at the bottom) to 
>> ~54VDC and we typically see ~49-51VDC at the top.  Yes, you can tweak the 
>> output of both the Meanwell and the Traco to compensate for voltage drop if 
>> needed.  
>> 
>> We use a Shireen hybrid fiber cable which has a 12AWG pair for DC.  We use 
>> these up to 200ft or so.
>> 
>> On Thu, Jun 20, 2019 at 3:47 PM Sterling Jacobson <sterl...@avative.net 
>> <mailto:sterl...@avative.net>> wrote:
>> So what’s the Traco parts list for that?
>> 
>>  
>> I don’t do this stuff normally, so excited to get started and try it out.
>> 
>>  
>> If I’m pushing 48v up top to a roof, what’s the voltage drop?
>> 
>>  
>> I assume these DC units can somehow be tweaked so that output can 
>> accommodate for voltage drop.
>> 
>>  
>> What size wire is everyone using typically for this, usually 30-100 ft max 
>> length?
>> 
>>  
>> I’m assuming it’s something like 10 AWG? At 48v and 5A and 50’ is maybe 
>> 47.5v at the end?
>> 
>> So I would push 49 or 50v just to be safe?
>> 
>>  
>> From: AF <af-boun...@af.afmug.com <mailto:af-boun...@af.afmug.com>> On 
>> Behalf Of Josh Baird
>> Sent: Wednesday, June 19, 2019 8:19 AM
>> To: AnimalFarm Microwave Users Group <af@af.afmug.com 
>> <mailto:af@af.afmug.com>>
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> FWIW - we have lots of EdgePoint S16's that are powered by Traco BCM/TSP 
>> combos @ ~54V with no issues.
>> 
>>  
>> I agree with others - your battery plant should be 48VDC.
>> 
>>  
>> On Wed, Jun 19, 2019 at 10:15 AM Sterling Jacobson <sterl...@avative.net 
>> <mailto:sterl...@avative.net>> wrote:
>> 
>> Yeah, I’ll probably just use 48v battery array in series and float higher.
>> 
>>  
>> That particular device can do 48v, it just may shut down POE if it gets 
>> lower than 48v.
>> 
>>  
>> From: AF <af-boun...@af.afmug.com <mailto:af-boun...@af.afmug.com>> On 
>> Behalf Of ch...@wbmfg.com <mailto:ch...@wbmfg.com>
>> Sent: Wednesday, June 19, 2019 8:11 AM
>> To: AnimalFarm Microwave Users Group <af@af.afmug.com 
>> <mailto:af@af.afmug.com>>
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> Why not run your system at 54 volts?  If the radio freaks out above 54, just 
>> set it at 54 and you should be fine.  Battery strings don’t exceed the float 
>> voltage of the rectifier.  If you are worried about it float at 53.75 volts. 
>> 
>>  
>> From: Sterling Jacobson
>> 
>> Sent: Tuesday, June 18, 2019 11:19 PM
>> 
>> To: AnimalFarm Microwave Users Group
>> 
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> Having a hard time figuring out the exact part/price for something like this.
>> 
>>  
>> Which Meanwell part would take 48v and make it 50v or 54v 5A?
>> 
>>  
>> From: AF <af-boun...@af.afmug.com <mailto:af-boun...@af.afmug.com>> On 
>> Behalf Of Adam Moffett
>> Sent: Tuesday, June 18, 2019 10:21 PM
>> To: af@af.afmug.com <mailto:af@af.afmug.com>
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> That's weird to me.  Any telecom equipment made for 48v I would have assumed 
>> they intended it to be used with a rectifier, and consequently I would 
>> assume it'd be ok up to at least 56v continuous; and maybe more like 60-70v 
>> for a short duration.  But yeah, DC-DC converter is the fix.
>> 
>> On 6/18/2019 11:36 PM, Sean Heskett wrote:
>> 
>> You need to use a DC-DC converter for sensitive equipment like that.  
>> Meanwell has a good selection.
>> 
>>  
>> On Tue, Jun 18, 2019 at 8:12 PM Sterling Jacobson <sterl...@avative.net 
>> <mailto:sterl...@avative.net>> wrote:
>> 
>> Apparently the UBNT EP-S16 freaks out if it goes above 54v.
>> 
>> Is there any way to assure it doesn’t float/charge above 54v, or maybe even 
>> just 50v?
>> 
>>  
>> From: AF <af-boun...@af.afmug.com <mailto:af-boun...@af.afmug.com>> On 
>> Behalf Of TJ Trout
>> Sent: Tuesday, June 18, 2019 7:26 PM
>> To: AnimalFarm Microwave Users Group <af@af.afmug.com 
>> <mailto:af@af.afmug.com>>
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> contact talley or tessco for a price, don't trust what you see on google, 
>> it's like 50% less
>> 
>>  
>> On Tue, Jun 18, 2019 at 6:25 PM TJ Trout <t...@voltbb.com 
>> <mailto:t...@voltbb.com>> wrote:
>> 
>> all 48v systems for battery power will float at 54v, it's also adjustable 
>> via the battery chemistry
>> 
>>  
>> On Tue, Jun 18, 2019 at 3:33 PM Sterling Jacobson <sterl...@avative.net 
>> <mailto:sterl...@avative.net>> wrote:
>> 
>> Ok, cool.
>> 
>>  
>> So can the 7bc2 be adjusted slightly to output 50v instead of just 48v?
>> 
>>  
>> There will be some loss going 100’  or so, right?
>> 
>>  
>>  
>> From: AF <af-boun...@af.afmug.com <mailto:af-boun...@af.afmug.com>> On 
>> Behalf Of TJ Trout
>> Sent: Tuesday, June 18, 2019 4:23 PM
>> To: AnimalFarm Microwave Users Group <af@af.afmug.com 
>> <mailto:af@af.afmug.com>>
>> Subject: Re: [AFMUG] UPS and DC to DC conversion
>> 
>>  
>> 12-54v is inefficient, if you want 200ah of battery use 4x50ah batteries for 
>> a 48v string
>> 
>> ICT24048-7BC2 360W 54v AC-DC + LVD + Charger
>> ICT-TMP - Temp sensor for charge compensation if batt's outside
>> ICT-WMB - Wall mount bracket
>> SITE Monitor - Voltage monitoring
>> 
>> Or
>> 
>> Alternativly;
>> 
>> 48v din mount PSU
>> 48v 'dc ups' to charge batt's and provide LVD
>> OR
>> 48v din 'dc ups' with integrated psu + lvd + charger (i.e. DIN-UPS 48-5 
>> cheaper options available)
>> 
>>  
>> On Tue, Jun 18, 2019 at 2:50 PM Sterling Jacobson <sterl...@avative.net 
>> <mailto:sterl...@avative.net>> wrote:
>> 
>> I’m trying to put a “box” system together for our house POP sites and need 
>> help with the DIN stuff and UPS.
>> 
>>  
>> Can you guys give me an idea or example of the following?
>> 
>>  
>> I want to take standard AC 15A in from a breaker outside the box.
>> 
>> And using maybe one or two 12v 105AH AGM batteries, supply 50v 6A up the 
>> side of the house.
>> 
>>  
>> I have never ordered DIN parts like this, guess I don’t have to use DIN, but 
>> would be nice.
>> 
>>  
>> Having a problem finding a DC to DC converter that takes 12v and upconverts 
>> to 50v 5-6A.
>> 
>>  
>> Is this the cost effective method? Something like this:
>> 
>>  
>> Monitoring         Sitemonitor Base Unit II SMON Base II                     
>>                                 1.00        $100.00                $100.00
>> 
>> UPS Monitor      Sitemonitor Int MorningStar MeterBus  SMON MorningStar      
>>    1.00        $60.00                 $60.00
>> 
>> UPS Charge         MorningStar Sunsaver Dual                                 
>>                                          1.00        $165.00                
>> $165.00
>> 
>> Battery AGM Deep Cycle 105AH NPP FT12-105AH                                  
>>                              2.00        $225.00                $450.00
>> 
>> DIN Parts like DC fuse/breakers and trunk stuff                              
>>                                     1.00        $100.00                
>> $100.00
>> 
>> DC 12v to 50v 5A                                                             
>>                                                                  1.00        
>> $150.00                $150.00
>> 
>> -- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
>> -- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
>> -- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
>>  
>>  
>> -- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
>> -- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>-- 
>> AF mailing list
>> AF@af.afmug.com <mailto:AF@af.afmug.com>
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
>> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
>> 
> 
> -- 
> AF mailing list
> AF@af.afmug.com <mailto:AF@af.afmug.com>
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com 
> <http://af.afmug.com/mailman/listinfo/af_af.afmug.com>
> -- 
> AF mailing list
> AF@af.afmug.com
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com

-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to