Look at 9.2.9 (19 Edition).
Sprinklers shall not be required to be installed in furniture  such  as  portable  wardrobe  units, cabinets,  trophy  cases, and  similar  items  not  intended for  occupancy.  This type of feature shall be permitted to be attached to the finished structure.

/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT

On 7/16/2026 3:31 PM, James Crawford wrote:

We have a project that is light hazard (office space) and they have a built in storage unit 18”x18”x18” cubicles inside with cabinet doors, it is 6’ wide and 7’6” high. It is totally recessed into the wall with no open space above, drywall to the ceiling.

I seem to remember something in the code about built in unit not requiring sprinkler protection but can’t find it., plus it seems very impractical to install 4 heads into this unit, one in each top cubical.

Any help would be appreciated.

Thank You

James Crawford

Phaser Fire Protection Ltd.