Look at 9.2.9 (19 Edition).
Sprinklers shall not be required to be installed in furniture such as
portable wardrobe units, cabinets, trophy cases, and similar
items not intended for occupancy. This type of feature shall be
permitted to be attached to the finished structure.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 7/16/2026 3:31 PM, James Crawford wrote:
We have a project that is light hazard (office space) and they have a
built in storage unit 18”x18”x18” cubicles inside with cabinet doors,
it is 6’ wide and 7’6” high. It is totally recessed into the wall with
no open space above, drywall to the ceiling.
I seem to remember something in the code about built in unit not
requiring sprinkler protection but can’t find it., plus it seems very
impractical to install 4 heads into this unit, one in each top cubical.
Any help would be appreciated.