Sprinklers Protect Floor Area at Density

.10gpm/ftsq  light havard
.2 gpm/ftsq  Ord Gp 2

if 36" or less floor area is OK

2022 handbook (see blue printing)
10.2.6.1.1.3 B

Chuck Bamford

On Mon, Jun 2, 2025 at 1:31 PM Ed Kramer <[email protected]> wrote:

> Getting the wording so the intent is clear is sometimes difficult.  Kudo’s
> to all who work on these standards.  I believe the intent is as Kyle
> describes it and I’ve attempted to illustrate an example in the attached.
>   The reason this section exists is illustrated in the top “ALL GOOD”
> sketch – it gives the designer more flexibility in the higher-ceiling area.
>
>
>
> Ed K
>
>
>
> *From:* Kyle.Montgomery <[email protected]>
> *Sent:* Monday, June 2, 2025 3:05 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: [External]Re: Ceiling Obstructions
>
>
>
> I think the confusion is coming from where the phrase “…provided the
> obstruction rules are observed…” is located in the sentence.
>
>
>
> When you read it like it’s written:
>
>
>
> “…provided the obstruction rules are observed as shown in Figure
> 8.6.4.1.1.3(B).”
>
>
>
> Then it sounds like the “obstruction rules” that you need to follow are
> what is shown in the figure. But I think the intent is to refer to the
> normal obstruction rules (such as the beam rule).
>
>
>
> Perhaps a better way to write it would be:
>
>
>
> “Provided the obstruction rules are observed, the sprinklers shall be
> permitted to be spaced as though the ceiling was flat as shown in Figure
> 8.6.4.1.1.3 (B).”
>
>
>
> At least, that’s what I think the intent is. Space it per the figure, but
> only if you meet the other obstruction rules.
>
>
>
> Are there any English majors on the NFPA 13 committee?
>
>
>
> *Kyle Montgomery*
>
>
>
> *Pre-Construction Manager*
>
> *Aero Automatic Sprinkler Co.*
>
> *21605 N. Central Ave.*
>
> *Phoenix, AZ 85024*
>
> *Direct: 623.580.7820*
>
> *Cell: 602.763.4736*
>
> [email protected]
>
>
>
>
>
>
>
> *From:* Anthony Johnson <[email protected]>
> *Sent:* Monday, June 2, 2025 11:34 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [External][Sprinklerforum] Re: Ceiling Obstructions
>
>
>
> Can you explain your reasoning for this conclusion? Why is this code there
> if you still have to use the obstruction rules? I'm interested in knowing
> if I've been interpreting this wrong.
>
>
>
> Anthony
>
>
>
> On Wed, May 28, 2025 at 9:35 AM Ed Kramer <[email protected]> wrote:
>
> Brain cramp or not, you are correct.
>
>
>
> Ed K
>
>
>
> *From:* Brian Harris <[email protected]>
> *Sent:* Wednesday, May 28, 2025 7:54 AM
> *To:* [email protected]
> *Subject:* [Sprinklerforum] Ceiling Obstructions
>
>
>
> Having a brain cramp this morning..
>
> (NFPA13 / 2013) There’s got to be more to Fig 8.6.4.1.1.3(b) with regard
> to ceiling height changes. For example, what if the head (blue arrow) is
> only a foot off the ceiling height change? I assume 8.6.5.1.2 would have to
> come into play as well?
>
>
>
>
>
> Thank you,
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssystemsinc.com
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to