I think the confusion is coming from where the phrase “…provided the 
obstruction rules are observed…” is located in the sentence.

When you read it like it’s written:

“…provided the obstruction rules are observed as shown in Figure 
8.6.4.1.1.3(B).”

Then it sounds like the “obstruction rules” that you need to follow are what is 
shown in the figure. But I think the intent is to refer to the normal 
obstruction rules (such as the beam rule).

Perhaps a better way to write it would be:

“Provided the obstruction rules are observed, the sprinklers shall be permitted 
to be spaced as though the ceiling was flat as shown in Figure 8.6.4.1.1.3 (B).”

At least, that’s what I think the intent is. Space it per the figure, but only 
if you meet the other obstruction rules.

Are there any English majors on the NFPA 13 committee?

Kyle Montgomery
 [cid:[email protected]]
Pre-Construction Manager
Aero Automatic Sprinkler Co.
21605 N. Central Ave.
Phoenix, AZ 85024
Direct: 623.580.7820
Cell: 602.763.4736
[email protected]<mailto:[email protected]>



From: Anthony Johnson <[email protected]>
Sent: Monday, June 2, 2025 11:34 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [External][Sprinklerforum] Re: Ceiling Obstructions

Can you explain your reasoning for this conclusion? Why is this code there if 
you still have to use the obstruction rules? I'm interested in knowing if I've 
been interpreting this wrong.

Anthony

On Wed, May 28, 2025 at 9:35 AM Ed Kramer 
<[email protected]<mailto:[email protected]>> wrote:
Brain cramp or not, you are correct.

Ed K

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Wednesday, May 28, 2025 7:54 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Ceiling Obstructions

Having a brain cramp this morning..
(NFPA13 / 2013) There’s got to be more to Fig 8.6.4.1.1.3(b) with regard to 
ceiling height changes. For example, what if the head (blue arrow) is only a 
foot off the ceiling height change? I assume 8.6.5.1.2 would have to come into 
play as well?

[cid:[email protected]]

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to