General Air has been providing listed air compressors for decades, they are
not the only one but we pretty much only use them for air compressors

https://www.generalairproducts.com/fire-protection-products/fire-protection-air-compressors/




Thanks



Brett Peters
General Manager Installation & Design
Proudline Fire Protection Services Ltd.
[email protected]
780 490 7602 office ext 202
780 490 7605 fax
780 777 0568 cell
780 718 2676 24h
Visit us at www.proudline.ca

Proudline now offers ULc listed monitoring services, please contact
[email protected] for more information


On Wed, May 14, 2025 at 2:28 PM Chris Dorn <
[email protected]> wrote:

> All,
>
>
>
> The 2025 NFPA 13 states the following:
>
> 8.2.7.5.2 *
> <https://codesonline.nfpa.org/code/search/8eb5977b-1437-474f-8319-29d916f8d741/np_33757375-bf9d-11ee-bf07-000d3a112b1a.html#ID000130010842>
>  Where an air compressor is dedicated for the sprinkler system, the air
> compressor shall be listed for fire protection.
>
>
>
> The appendix further clarifies:
>
> A.8.2.7.5.2  Temporary use of non-listed air compressors should be
> permitted when listed compressors are not immediately available.
>
>
>
> Is the device required to be listed as an assembly? I would assume so but
> I’m having trouble finding compressors that carry a listing. I see where
> the pressure switch might be listed or the motor carries a listing but I
> see no “listed” compressors. Anyone that can clarify what the listing
> requirement actually is?
>
>
>
> Thank you,
>
> Chris
>
>
>
>
>
>
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to