Hi James,

You're not missing anything - you're correct. Standard design area density 
curves (e.g., 0.30 gpm/ft² over 2000 ft²) do not apply to EEGAP rack storage. 
This type of commodity has a very high heat release rate, and NFPA 13 
recognizes that area-density curves aren't suitable for:

  *   Rack storage
  *   High challenge plastics
  *   ESFR protection
  *   In-rack sprinkler configurations
Instead, Chapters 25 through 27 of NFPA 13 (2022 or 2019 edition) outline 
specific protection schemes tailored to:

  *   The type of plastic
  *   The storage height
  *   The rack configuration
  *   The ceiling height
  *   The presence and arrangement of in-rack sprinklers

Regards,
Yasser Amer

From: James Crawford <[email protected]>
Sent: Monday, April 28, 2025 11:10 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Exposed Expanded Group A Plastics


! External Email, Use Caution !

We are looking at a refrigeration storage facility that is looking at a new 
client and they want to make sure they can use the space and asked s to have a 
look.

The new client will be storing fish in exposed expanded Group A plastic 
coolers, and these will be stored on single, double and multi row racks.

The existing sprinkler system is designed to 0.30usgpm over 2000 ft² plus two 
levels of in-rack sprinklers.

I cannot find any protection schemes for design area applications that will 
provide protection schemes for the exposed expanded Group A plastics. Is there 
something I am missing or can someone point me in the right direction.

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: http://www.phaserfire.ca/<http://www.phaserfire.ca/>


________________________________



Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system.

While Dar and the Dar Group strive to maintain high standards of communication, 
reliability, authenticity and integrity, neither shall be liable for the 
improper or incomplete transmission of the information contained in this 
communication nor for any delay in its receipt or damage to your system. 
Neither Dar nor the Dar Group guarantees that the integrity of this 
communication has been maintained or that this communication is free of 
viruses, interceptions or interference.

Confidentiality & Disclaimer Note: This e-mail (including any attachments) 
contain protected and confidential information intended for the sole use of the 
individual or organization addressee. If you are not the addressee or an 
authorized agent acting on their behalf, or if you have received this message 
by error, please notify the sender immediately be returning the message. It 
must not be copied, distributed or used in any other way but should be 
immediately deleted from your system. While Dar and the Dar Group strive to 
maintain high standards of communication, reliability, authenticity and 
integrity, neither shall be liable for the improper or incomplete transmission 
of the information contained in this communication nor for any delay in its 
receipt or damage to your system. Neither Dar nor the Dar Group guarantees that 
the integrity of this communication has been maintained or that this 
communication is free of viruses, interceptions or interference.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to