NFPA 13 2025 edition has 23.4 for Exposed Expanded Grp A plastics. But I don't know if you will be compatible with a refrigerated space. Tyco makes a K25 dry pendent ESFR.
It may not be the pipe sizes you want to see. I don't know if dry pendents are an option in your facility. Travis Mack, SET M.E.P.CAD | Instructor / Support 181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074 www.mepcad.com<http://www.mepcad.com/> | 303-923-8215 Email: [email protected] AutoSPRINK | AutoSPRINK FAB | AutoSPRINK RVT | AlarmCAD Academy of Fire Sprinkler Technology | Director, Engineering Technology 101 S Main Street, Suite 001, Decatur, IL 62523 ________________________________ From: James Crawford <[email protected]> Sent: Monday, April 28, 2025 3:09 PM To: Discussion list on issues relating to automatic fire sprinklers <[email protected]> Subject: [Sprinklerforum] Exposed Expanded Group A Plastics We are looking at a refrigeration storage facility that is looking at a new client and they want to make sure they can use the space and asked s to have a look. The new client will be storing fish in exposed expanded Group A plastic coolers, and these will be stored on single, double and multi row racks. The existing sprinkler system is designed to 0.30usgpm over 2000 ft² plus two levels of in-rack sprinklers. I cannot find any protection schemes for design area applications that will provide protection schemes for the exposed expanded Group A plastics. Is there something I am missing or can someone point me in the right direction. Thank You James Crawford Phaser Fire Protection Ltd. Phone 604-888-0318 Cel: 604-790-0938 Email [email protected]<mailto:[email protected]> Web: www.phaserfire.ca<http://www.phaserfire.ca>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]