JD, I interpreted “room” as being the room where the spraying is done.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
  
>   
> On Apr 9, 2025 at 8:05 AM,  <JD Gamble (mailto:[email protected])>  
> wrote:
>   
>   
>         
>   
>
> Doesn’t code require any “room” in which spray operations are conducted to be 
> fully sprinkled?
>
>   
>
>   
>
>   
>
>  NFPA 33: 2018 ed. - 4.1.1* Locations in Other Occupancies.    Spray 
> application operations and processes shall not be conducted in any building 
> that is classified as an assembly, an educational, a day care, a health care, 
> an ambulatory health care, a detention/correctional, a residential, a 
> mercantile, a business, or a storage occupancy, unless the following 
> requirements are met:
>
>   
>
>    (1) The spraying is located in a room that is separated both
>
>   
>
>    vertically and horizontally from all surrounding areas by
>
>   
>
>    construction having a fire resistance rating of not less
>
>   
>
>    than 2 hours or in a spray room    (see Section 5.2).
>
>   
>
>    (2) The room is protected by an approved automatic sprinkler
>
>   
>
>    system designed and installed in accordance with
>
>   
>
>  NFPA 13.
>
>   
>
>   
>
>   
>   
>   
>
> From:   Fpdcdesign  <[email protected]>
>   Sent:  Wednesday, April 9, 2025 5:46 AM
>   To:  Sprinklerforum  <[email protected]>
>   Subject:  [Sprinklerforum] Phantom flow on partial system.
>
>   
>   
>   
>
>   
>
>   
>   
>
> I am working on a 4500 sqft commercial building that is presently 
> unsprinklered. There is no plan or requirement to install a full system at 
> this point. The building is to be occupied as an auto body shop. There is an 
> existing 14x24 spray booth that has a system fed from the 2” domestic. There 
> is a system in the spray booth that is neither complete nor hydraulically 
> correct. I am in the process of re-designing it.   
>
>   
>   
>   
>
>   
>
>   
>   
>   
>
> The spray booth requires 4 sprinklers and the exhaust stack, one. The design 
> criteria is Extra Hazard 2. The sprinkler flow for the 5 sprinklers is 178 
> gpm. If I look at the “Phantom Flow” requirements, that would result in an 
> additional 822 gpm to be added at the point where the furthest branch line 
> meets the cross main to make the 1000 gpm. First of all, is this really 
> required? Secondly, this seems ridiculous to do this in an otherwise 
> unsprinklered building. What purpose does it serve?   
>
>   
>   
>
>   
>
>   
>   
>   
>
> Todd G Williams, PE
>
>   
>   
>
> Fire Protection Design/Consulting
>
>   
>   
>   
>
> Stonington, CT
>
>   
>   
>   
>
> 860-535-2080 (tel:860-535-2080)   (ofc)
>
>   
>   
>   
>
> 860-554-7054 (tel:860-554-7054)     (fax)
>
>   
>   
>   
>
> 860-608-4559 (tel:860-608-4559)   (cell)
>
>   
>   
>   
>   
>  _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]
>   
  
  
     