I think your biggest hurdle will be getting the water delivery time of 15 seconds. NFPA 13 2019 8.2.6.3.
Taylor Schumacher From: Jay Google <[email protected]> Sent: Thursday, April 03, 2025 6:26 AM To: Sprinkler Forum <[email protected]> Subject: [Sprinklerforum] Changing Antifreeze to Dry System We have a customer that wants to change the existing antifreeze to a dry system. All the sprinklers on the system are pendents on drops. It is a pipe schedule system. I think the best way to do this is keep the existing piping, chang Warning: Unusual sender <[email protected]<mailto:[email protected]>> You don't usually receive emails from this address. Make sure you trust this sender before taking any actions. We have a customer that wants to change the existing antifreeze to a dry system. All the sprinklers on the system are pendents on drops. It is a pipe schedule system. I think the best way to do this is keep the existing piping, change the sprinklers and verify the pipe is pitched correctly to drain as required or add low point drains if needed. This way the sprinklers line up with existing holes from the attic. The building is an independent living building (light hazard/residential). My questions are 1) does the system need to be calculated since it's a pipe schedule and 2) If so, can we use the room design method on a dry system? We are on the 2019 edition of NFPA 13. I did not see anything in chapter 19 on using room design for dry systems and don't recall ever seeing that. With that in mind, if we calculate the 1950 sq. ft., there are a lot of closets included in that that kill the calculations. The building was built in 1999, of course no drawings and the pipe looks as good as new inside and out. Jay Stough Tustin Fire Solutions
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]