We are having this same conversation regarding hydraulic test of manual dry 
standpipe systems in parking garages.

NFPA-25 (2023) § 6.3.1.1 is only applicable to Automatic Systems, not Manual 
Systems.



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Brandon Bridgford <[email protected]>
Sent: Friday, February 28, 2025 12:43 PM
To: [email protected]
Subject: [Sprinklerforum] Class 1 Flow Test

Good Afternoon, I am performing a 5-year flow test for a single-story data 
center that has 2. 5” outlets through the hallways. The calc plate says it is 
designed for a discharge rate of 1000gpm, when supplied with water at the rate 
of 1250gpm

Good Afternoon,

I am performing a 5-year flow test for a single-story data center that has 2.5” 
outlets through the hallways. The calc plate says it is designed for a 
discharge rate of 1000gpm, when supplied with water at the rate of 1250gpm at 
69psi at the base of the riser. Hose stream allowance of 1000gpm is included.

There is no fire pump, and the static pressure is approximately 72psi. I flowed 
the farthest outlet with a flow meter, and I was able to get 425gpm with a 
residual of 62 at the base of the riser. The AHJ wants testing to be performed 
per NFPA 25. Would this mean I need to flow 1000 or 1250gpm simultaneously? I 
will need a pump truck to achieve these numbers.

Any thoughts or advice would be greatly appreciated. Thank you!


[cid:[email protected]]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to