High Expansion Foam Generators are equipped with fans.  Typical usage is 
aircraft hangars or warehouses.
Foam Chambers commonly are triangular in shape or cans approximately 1-2 
gallons in capacity, typically mounted on flammable liquids storage tanks.
Bladder tanks do not utilize foam pumps.  The pump you described sounds like a 
fire pump (NFPA-20).  Foam pumps take suction from an atmospheric foam 
concentrate tanks.



Thank you,

Jackie “JW” Ward
1-405-240-7076

From: Tim Easter <[email protected]>
Sent: Thursday, February 20, 2025 6:59 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] NFPA 11 and 25

Are high expansion foam generators considered fixed foam devices? We are using 
fire pumps to pressurize the bladder tank, thru proportioner attached to riser. 
Are these pumps considered water-powered foam concentrate pumps? How do I know 
if

Are high expansion foam generators considered fixed foam devices? We are using 
fire pumps to pressurize the bladder tank, thru proportioner attached to riser. 
Are these pumps considered water-powered foam concentrate pumps? How do I know 
if I have a foam chamber, a diaphragm balancing valve, a vacuum vent, or a 
rupture disk? How do I know if the foam concentrate tank, which is a bladder 
tank, has an expansion dome? Is HEF generator considered a foam maker?
Thanks.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to