Just getting 18” above the tray doesn’t alleviate the tray from being an 
obstruction to the discharge pattern of the sprinklers.  It’s a little more 
complicated than that.

Also, is this actually tray or ladder racking, one is solid the other is open.  
How wide is the tray?  If is actually rack, how densely packed is it going to 
be?

Cable trays can be any size and can actually end up needing sprinklers below 
just like you’d do with HVAC duct.

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Anthony Carrizosa <[email protected]>
Sent: Tuesday, February 11, 2025 12:22 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Server room

Can you ask them to raise the ceiling a few inches to get you a minimum of 18” 
above the cable tray? Other wise tell them you have to add sprinklers below the 
cable tray and right on top of the servers. That should get them to be willing 
to

Can you ask them to raise the ceiling a few inches to get you a minimum of 18” 
above the cable tray? Other wise tell them you have to add sprinklers below the 
cable tray and right on top of the servers. That should get them to be willing 
to move the ceiling up.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]




From: Tim Easter <[email protected]<mailto:[email protected]>>
Sent: Tuesday, February 11, 2025 9:06 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Server room

I have a server room that is 10' ceiling. The cable tray sits atop the servers 
at 8-8". I plan on using NFPA 13, 2022 edition, section 10.2.7.3.2.3 and figure 
10.2 7.3.2.3. What does it mean in figure, "center of partition less than 12"? 
Servers are larger than 12", so I cannot use this method? Must resort to 3* 
rule?

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to