Can you ask them to raise the ceiling a few inches to get you a minimum of 18” 
above the cable tray? Other wise tell them you have to add sprinklers below the 
cable tray and right on top of the servers. That should get them to be willing 
to move the ceiling up.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]




From: Tim Easter <[email protected]>
Sent: Tuesday, February 11, 2025 9:06 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Server room

I have a server room that is 10' ceiling. The cable tray sits atop the servers 
at 8-8". I plan on using NFPA 13, 2022 edition, section 10.2.7.3.2.3 and figure 
10.2 7.3.2.3. What does it mean in figure, "center of partition less than 12"? 
Servers are larger than 12", so I cannot use this method? Must resort to 3* 
rule?