Please keep in mind if an underground supply a fire pump system, the
minimum velocity is 15 fps.  While I do not agree with this requirement,
iut is in the book.

Thanks,
John

John August Denhardt, PE
*Vice President, Engineering and Technical Services*

*American Fire Sprinkler Association*
m: p: 301-343-1457
214-349-5965 ext 121
w: firesprinkler.org



Kickstart 2025 with Top-TIer Training!

AFSA is offering a variety of training to start 2025 off right! Learn
design, hydraulic calculations, and ITM with our best-in-class training.
Learn more and register now for the February Beginning Design School
<https://www.firesprinkler.org/design>, Sprinkler Hydraulics Course
<https://www.firesprinkler.org/programs/calculations/>, Fire Pump ITM
<https://www.firesprinkler.org/calendarevent/fire-pump-itm-workshop-9/>,
and Beginning ITM workshop
<https://www.firesprinkler.org/calendarevent/beginning-itm-workshop-6/>!




On Tue, Jan 28, 2025 at 5:36 PM Brett Peters <[email protected]> wrote:

>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
> If this is for a new water main, the intent of this flush is to get rid of
> any debris and sediment that would be harmful to the sprinkler system, so
> if you have a 6" water service you need to achieve minimum flow for 6" pipe
> to adequately flush sediment and debris from the underground piping
>
> 10.10.2.1.3 The minimum rate of flow shall be not less than
> one of the following:
> (1) Hydraulically calculated water demand flow rate of the
> system, including any hose requirements
> (2) Flow necessary to provide a velocity of 10 ft/sec
> (3.1 m/sec) in accordance with Table 10.10.2.1.3
> (3) Maximum flow rate available to the system under fire
> conditions
>
> 880gpm for 6" pipe, to produce 10 ft/sec
>
> If flowing a fire pump you would need to open 2 x 2 1/2" hose valves for
> that amount of flow so I'm very sceptical that a single 1 1/2" hose will
> produce the amount of flow required for a proper flush, personally when I
> have done a flush for a 6" water service we have flushed with 4"
>
>
>
>
> Thanks
>
>
>
> Brett Peters
> General Manager Installation & Design
> Proudline Fire Protection Services Ltd.
> [email protected]
> 780 490 7602 office ext 202
> 780 490 7605 fax
> 780 777 0568 cell
> 780 718 2676 24h
> Visit us at www.proudline.ca
>
> Proudline now offers ULc listed monitoring services, please contact
> [email protected] for more information
>
>
>
>
>
>
> On Tue, Jan 28, 2025 at 3:11 PM Steve Leyton <[email protected]>
> wrote:
>
>> Sprinkies:
>>
>> Section 6.10.2.1 (2022 edition) of NFPA 13 prescribes a minimum flow rate
>> of 10 fps for flushing, and Table 6.10.2.1.3 offers flow minimum rates for
>> different pipe diameters that will achieve that velocity.   My question is
>> (the one that’s been posed to me by an inspector) is whether or not there’s
>> an absolute minimum flow rate in GPM based on size.   A contractor has
>> proposed to flush a 4” UG through a 1½” connection with “several hundred
>> feet” of 1½” hose to a collection point.   The inspector is questioning
>> (and I’m wondering also) if it is required or is the intent to flush to at
>> least the demand of the system, or some other benchmark flow?   For
>> whatever it’s worth Table 6.10.2.1.3 (10.10.2.1.3 in NFPA 24) starts at 2”,
>> so I’m also curious if that implies that 2” is the minimum allowable size
>> for a flushing connection?
>>
>>
>>
>> *Steve Leyton, President*
>> T  *|*  619.255.8964 x 102  *| *
>> *www.protectiondesign.com <http://www.protectiondesign.com/> *2851
>> Camino Del Rio South  *|*  Suite 210  *|*  San Diego, CA  92108
>> Fire Protection System Design *|* Consulting *|* Planning *|* Training
>>
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to