FWIW this was changed from 2019 to 2022, it previously stated “enclosed with 
walls” interior was added in 2022 with the justification that the intent was 
not to require exterior walls to be rated and carried without dissent or 
comment.  Ref: FR 1230-NFPA 13-2019.

Mike Morey
CFPS 3229 • NICET S.E.T. 123677
Project Estimator • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive • Fort Wayne, IN • 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]

From: Jeff Brickell <[email protected]>
Sent: Friday, January 24, 2025 2:55 PM
To: [email protected]
Subject: [Sprinklerforum] Room Design Method

Good afternoon. I have an apartment project that has a small room that contains 
a diesel-powered generator. The room is on the corner of the building on level 
1 and contains two interior walls, and two exterior walls. The two interior 
walls
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
Good afternoon.  I have an apartment project that has a small room that 
contains a diesel-powered generator.  The room is on the corner of the building 
on level 1 and contains two interior walls, and two exterior walls.  The two 
interior walls are rated 2-HR, as well as the ceiling, however, the two 
exterior walls are rated 1-HR.  The room only has one door that opens to the 
exterior.

I asked the architect to upgrade the two exterior walls to a minimum of 90 
minutes to meet the water supply duration requirements of EH2 (it is a 
monitored system) so that I could use the Room Design Method.  He is pushing 
back and asked why I wanted him to do that.

As most of you know, The Room Design method requires “The enclosing interior 
walls of such a room must provide a fire resistance rating equal to the water 
supply duration requirements of Table 
19.2.3.1.2<https://urldefense.com/v3/__https:/link.nfpa.org/publications/13/2025/chapters/19*ID000130002953__;Iw!!FaxH778!fVK3OkoiQ8wAG01O6JM74bvFC524lSCGK3wteU2rqB_0-9rSlLDc3ywpfLl5XkjQigXptxWl2KYQQ5Y$>”.

His argument to not upgrade the fire rating of the exterior walls is that the 
code says ‘interior walls’, and not all walls, or exterior walls.  I’m 
explaining to him that the walls are interior to the room itself, but he is not 
hearing me.   Is there any other definitions or areas of NFPA I can cite that 
would make him understand what I and the code is saying?  Am I misreading it?  
I have not applied the Room Design Method yet, but it seems cut and dry unless 
I’m missing something.

Any advice helps!  Thank you.


Jeff Brickell, CET
Senior Estimator/Designer
NICET III CERTIFIED
CERT #147245

OREGON CERTIFIED COBID FIRM #13272
(EMERGING SMALL BUSINESS)

TRIAD FIRE PROTECTION
[cid:[email protected]]
OREGON . WASHINGTON . ARIZONA

OFFICE  503.856.6333
CELL       602.550.4292
FAX        866.766.8862


This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to