Good afternoon.  I have an apartment project that has a small room that 
contains a diesel-powered generator.  The room is on the corner of the building 
on level 1 and contains two interior walls, and two exterior walls.  The two 
interior walls are rated 2-HR, as well as the ceiling, however, the two 
exterior walls are rated 1-HR.  The room only has one door that opens to the 
exterior.

I asked the architect to upgrade the two exterior walls to a minimum of 90 
minutes to meet the water supply duration requirements of EH2 (it is a 
monitored system) so that I could use the Room Design Method.  He is pushing 
back and asked why I wanted him to do that.

As most of you know, The Room Design method requires “The enclosing interior 
walls of such a room must provide a fire resistance rating equal to the water 
supply duration requirements of Table 
19.2.3.1.2<https://link.nfpa.org/publications/13/2025/chapters/19#ID000130002953>”.

His argument to not upgrade the fire rating of the exterior walls is that the 
code says ‘interior walls’, and not all walls, or exterior walls.  I’m 
explaining to him that the walls are interior to the room itself, but he is not 
hearing me.   Is there any other definitions or areas of NFPA I can cite that 
would make him understand what I and the code is saying?  Am I misreading it?  
I have not applied the Room Design Method yet, but it seems cut and dry unless 
I’m missing something.

Any advice helps!  Thank you.


Jeff Brickell, CET
Senior Estimator/Designer
NICET III CERTIFIED
CERT #147245

OREGON CERTIFIED COBID FIRM #13272
(EMERGING SMALL BUSINESS)

TRIAD FIRE PROTECTION
[cid:[email protected]]
OREGON . WASHINGTON . ARIZONA

OFFICE  503.856.6333
CELL       602.550.4292
FAX        866.766.8862

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to