No it does not mean non combustible but it can mean “limited combustible” which as I’m sure you know can effect the design. 

Again, I would have a FPE make the determination in this case.

Mike Stewart
Dog Walker 

On Nov 14, 2024, at 12:07 PM, Steele, Andrew <[email protected]> wrote:



If interested, Internation Building Code has guidance for “children’s indoor play structures”, in the 2018 IBC, look at section 424.  “Fire treated” doesn’t mean non-combustible.  

 

CHAPTER 4 SPECIAL DETAILED REQUIREMENTS BASED ON OCCUPANCY AND USE - 2018 INTERNATIONAL BUILDING CODE (IBC)

 

Andrew Steele,

 

 

From: Mike Stewart <[email protected]>
Sent: Wednesday, November 13, 2024 2:14 PM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: [External]Re: Jump Park

 

You don't often get email from [email protected]. Learn why this is important

I’ve heard this argument before…”Trampolines are plastic and therefore should be treated as such.” However, typical fire sprinkler designers and AHJ’s are unaware that a lot of trampolines and even trampoline pits contain flame retardants. People such as Trampoline Parks LLC use fire retardants in their vinyl wrap as well as well as in their safety nets and trampoline pads.

 

And while we are on the subject, even a lot of the trampoline pits that contain foam cubes are treated with flame retardants as well. 

 

Don’t be like most of the know it all, knuckle dragging, and mentally challenged individuals in the industry and go ahead and have the owner spend the $500-$750 and have a fire protection engineer make a determination. Oh…and that same engineer probably has a heck of a lot of more insurance to back his/her decision on what is truly needed. 

 

Mike Stewart

Dog Walker

 

On Nov 13, 2024, at 1:56 PM, Fpdcdesign <[email protected]> wrote:



Several years ago I did a large indoor playground (4000+ sqft). They had some larger pieces of equipment both wood and plastic. There were a couple of spaces that were actually storage rooms. The rooms got sprinklers. A lot of the unenclosed spaces didn’t because they were places kids would be playing, but were considered obstructions. Sprinklers in those spaces could be easily damaged by the kids. 

 

We came to a compromise between myself (PE), the AHJ and the tenant on a system design. That may be the approach you need to take

 

I am not going to post details of the final solution on a public forum for liability reasons. 

 

Todd Williams 

Fire Protection Design/Consulting

Stonington, CT

860-608-4559




On Nov 13, 2024 at 1:21 PM, <Craig Prahl> wrote:

Yes, everything is plastic.  But it also has to meet specific smoke spread and heat release ratings along with other construction requirements.

 

The Building code defines the requirements for the materials used in these playgrounds.  But note, this section is only applicable based on the defined dimensions. 

 

Regarding fire sprinklers, the IBC states the following:

[F] 424.3 Fire protection. Children’s play structures shall be provided with the same level of approved fire suppression and detection devices required for other structures in the

same occupancy.

 

So, notice the word “approved” in that sentence?  That means that the proposed protection scheme is to be approved by the AHJ. 

 

The big problem with the way the sentence is structured is that it doesn’t say one way or another whether you should install sprinklers below obstructions within the playground array like you would elsewhere. 

 

So as the sprinkler designer, ask for vendor data on the assembly and see how it aligns with the code requirements.  Then propose your design to the AHJ based on the basis of design. 

 

Craig Prahl | Jacobs | Fire Protection SME – EV, AM, DC, Special Hazards

[email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS

 

 

From: Kyle.Montgomery <[email protected]>
Sent: Wednesday, November 13, 2024 9:49 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: [External]Re: Jump Park

 

I don’t want to be the guy. But I’m guessing someone is going to jump in (pun intended) and say “Hey, is that jungle gym made out of plastic?” And then question whether the overhead system is even appropriate for this use.

 

-Kyle Montgomery

Innocent Bystander

 

From: Mike Stewart <[email protected]>
Sent: Tuesday, November 12, 2024 11:59 AM
To: Discussion list on issues relating to automatic fire sprinklers <[email protected]>
Subject: [External][Sprinklerforum] Re: Jump Park

 

You don't often get email from [email protected]. Learn why this is important

NFPA 13 is not entirely clear about this because obviously a trampoline should not be compared to a conference room table. Anytime an AHJ brings something like this up and NFPA 13 is not clear about it that’s when I hire a FPE to take a look at it and make an interpretation. This is just so the local AHJ has something to protect them just in case there is something such as a fire.

 

Mike Stewart

Dog Walker 

 

On Nov 12, 2024, at 1:28 PM, Brett Peters <[email protected]> wrote:



That's a tough one, is it actually fixed in place? If not it could be considered as a non combustible obstruction, not fixed in place, thus not requiring sprinklers below - but that might be a stretch.

 

NFPA 13, 2019

 

9.5.5.3.2* Sprinklers shall not be required under obstructions that are not fixed in place, such
as conference tables.
The size at which obstructions become too large to ignore is typically 4 ft (1.2 m). This width is reduced in
Chapters 13 and 14 for CMSA and ESFR sprinklers. Paragraph 9.5.5.3.2 recognizes that some obstructions
larger than 4 ft (1.2 m), for example, a conference table, are not fixed in place and are not likely to have any
significant combustibles located beneath them. In such cases, additional sprinklers are not needed below
the obstruction.

 

 

Thanks

 

 

 

Brett Peters

General Manager Installation & Design

Proudline Fire Protection Services Ltd.

780 490 7602 office ext 202

780 490 7605 fax

780 777 0568 cell

780 718 2676 24h

Visit us at www.proudline.ca

 

Proudline now offers ULc listed monitoring services, please contact [email protected] for more information

 

 

 

       

 

 

On Tue, Nov 12, 2024 at 11:09 AM Caleb Brogan <[email protected]> wrote:

Hello,

 

We have an indoor jump park where they put in a jungle gym with the netting all the way around it, the padded walkways are 4’ wide exactly. There are 2 slides on it, one 8’ wide and one 5’ wide. There is ceiling protection above it currently, has anyone put sprinklers anywhere down inside of these? Having a hard time finding much information on it other than “if the local AHJ requires it”, but the local AHJ is worried, not mandating it so looking for a little direction.

 

Thanks,

Caleb

Caleb Brogan | Sprinkler Systems Designer
OH# 54-25-4815 & NICET# 147230 
KOORSEN FIRE & SECURITY
727 Manor Park Dr, Columbus, OH 43228
P 614.853.5665
| Ext. 6512 | M 614.867.6791
[email protected] 
| www.koorsen.com  

24x7x365 Service: 614.878.2228 | [email protected]    


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

CAUTION: This email originated from outside of our organization. Do not click links or open attachments unless you recognize the sender and know the content is safe.


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to