That's a tough one, is it actually fixed in place? If not it could be considered as a non combustible obstruction, not fixed in place, thus not requiring sprinklers below - but that might be a stretch.
NFPA 13, 2019 9.5.5.3.2* Sprinklers shall not be required under obstructions that are not fixed in place, such as conference tables. The size at which obstructions become too large to ignore is typically 4 ft (1.2 m). This width is reduced in Chapters 13 and 14 for CMSA and ESFR sprinklers. Paragraph 9.5.5.3.2 recognizes that some obstructions larger than 4 ft (1.2 m), for example, a conference table, are not fixed in place and are not likely to have any significant combustibles located beneath them. In such cases, additional sprinklers are not needed below the obstruction. Thanks Brett Peters General Manager Installation & Design Proudline Fire Protection Services Ltd. [email protected] 780 490 7602 office ext 202 780 490 7605 fax 780 777 0568 cell 780 718 2676 24h Visit us at www.proudline.ca Proudline now offers ULc listed monitoring services, please contact [email protected] for more information On Tue, Nov 12, 2024 at 11:09 AM Caleb Brogan <[email protected]> wrote: > Hello, > > > > We have an indoor jump park where they put in a jungle gym with the > netting all the way around it, the padded walkways are 4’ wide exactly. > There are 2 slides on it, one 8’ wide and one 5’ wide. There is ceiling > protection above it currently, has anyone put sprinklers anywhere down > inside of these? Having a hard time finding much information on it other > than “if the local AHJ requires it”, but the local AHJ is worried, not > mandating it so looking for a little direction. > > > > Thanks, > > Caleb > > Caleb Brogan | Sprinkler Systems Designer > OH# 54-25-4815 & NICET# 147230 > > *KOORSEN FIRE & SECURITY*727 Manor Park Dr, Columbus, OH 43228 > P 614.853.5665 | Ext. 6512 | M 614.867.6791 > [email protected] | www.koorsen.com > > *24x7x365 Service: 614.878.2228* | [email protected] > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected] >
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]