NFPA 13, 2013 ed  Section 17.3.1 - control mode area-density sprinkler 
protection
I have a 80ft tall existing building where they want to install single and 
double row racks to 40ft of storage of cartooned  / exposed Group A 
non-expanded plastics.
I don't see a maximum clearance height between the top of storage and the 
ceiling in this section.  Am I missing something?
What's confusing is that if you look at chapter 16.3 (rack storage of Class 
I-IV over 25ft)you see 10ft maximum between top to storage and ceiling all over 
the place.
Yet if I design per 17.3.1 it is also good for Class I-IV commodities.

Thank you,