Have a rated wall or walls installed between sections and use room design 
method?
Ed K


From: Fpdcdesign <[email protected]>
Sent: Monday, June 24, 2024 9:52 AM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Reducing dry system area

I am working on a building with a unique facad where I am trying to figure out 
the calcs. Each end of the building has a 24x24 “tower” where the roof slope on 
4 sides to a peak. The center of the building over the entry has a 24x17 
inverted V sloped roof. Connecting each of these is a mansard. All construction 
is combustible. The roof slopes are 7:12. The total area is approximately 2000 
sqft.

The sections are separated by a plywood barrier.

The occupancy is Light Hazard. It’s is a dry system so I have to increase the 
RA by 30%. Since the slopes are steep enough, I have to increase another 30%, 
for a total of 2535 sqft design area.

My layout consists of 27 sprinklers (including 3 attic AS in the center 
section). No realistic way to decrease due to the arrangement. This totally 
blows out that calc with a 27 sprinkler flow.

Any thoughts on how to decrease the number of sprinklers flowing? I have tried 
all of my tricks but haven’t come up with anything yet.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080<tel:860-535-2080> (ofc)
860-554-7054<tel:860-554-7054>  (fax)
860-608-4559<tel:860-608-4559> (cell)