I am working on a building with a unique facad where I am trying to figure 
out the calcs. Each end of the building has a 24x24 “tower” where the roof 
slope on 4 sides to a peak. The center of the building over the entry has a 
24x17 inverted V sloped roof. Connecting each of these is a mansard. All 
construction is combustible. The roof slopes are 7:12. The total area is 
approximately 2000 sqft.   
  

  
The sections are separated by a plywood barrier.   
  

  
The occupancy is Light Hazard. It’s is a dry system so I have to increase the 
RA by 30%. Since the slopes are steep enough, I have to increase another 30%, 
for a total of 2535 sqft design area.   
  

  
My layout consists of 27 sprinklers (including 3 attic AS in the center 
section). No realistic way to decrease due to the arrangement. This totally 
blows out that calc with a 27 sprinkler flow.   
  

  
Any thoughts on how to decrease the number of sprinklers flowing? I have tried 
all of my tricks but haven’t come up with anything yet.   
  
  
  
Todd G Williams, PE  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-535-2080 (tel:860-535-2080)  (ofc)
  
860-554-7054 (tel:860-554-7054)     (fax)
  
860-608-4559 (tel:860-608-4559)  (cell)
  
  
  
  

  
     