Steve,
Yes there is a hose connection at the first floor landing of the remote stand 
pipe. Yes there is access to occupied first floor space via the exit passage 
and the remote stairway.
Thanks

Christopher S. Wilson SET
Project Design Manager
Treasure Valley Fire Protection
2731 S. Saturn Way
Boise, ID 83709
Phone:  208-362-1888
Fax: 208-362-2207

please note all TVFP email
addresses have changed
new email below

[email protected]<mailto:[email protected]>

From: Steve Leyton <[email protected]>
Sent: Friday, May 10, 2024 7:29 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Standpipe NFPA14 2019

Do you have a hose connection on the 1st floor landing of the remote standpipe 
stairwell in addition to the one at the exit passageway door?   And is there 
access to occupiable areas on the first floor from the passageway or stairwell?

Obviously, two or more hose connections supplied by a feed main on a single 
floor is a horizontal standpipe by definition, but it would seem to me that in 
this type of egress system that would be redundant or not of value depending on 
where a firefighter would be going with the water after connection to one or 
the other hose connection.

The foregoing does not represent any opinion or interpretation of the standard 
on behalf of NFPA or the NFPA 14 Technical Committee.

[cid:[email protected]]
Steve Leyton, President
T  |  619.255.8964 x 102  |  
www.protectiondesign.com<http://www.protectiondesign.com/>
2851 Camino Del Rio South  |  Suite 210  |  San Diego, CA  92108
Fire Protection System Design | Consulting | Planning | Training



From: Chris Wilson [mailto:[email protected]]
Sent: Friday, May 10, 2024 7:42 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Standpipe NFPA14 2019


To all,
I have a 4 story building with 2 exit stairways I am installing a class I 
manual wet standpipe combination sprinkler system. The remote stair is on the 
interior of the building and has a rated exit passageway  on the first floor 
that is 73' long. I am placing all hose valves on the main floor landings and 
one a the exit door of the exit passage way.

I am planning on calculating 500 gpm from the remote stand pipe and 250 for the 
2nd standpipe. The exit passage way hose connection will be fed by a  2/12 
lateral pipe fed from the  4" horizontal supply to the remote standpipe as it 
pass by the exit passageway.

Do I need to include an additional 250 gpm in my calcs at the hose valve at the 
exit passageway?

Thanks
Christopher S. Wilson SET
Project Design Manager
Treasure Valley Fire Protection
2731 S. Saturn Way
Boise, ID 83709
Phone:  208-362-1888
Fax: 208-362-2207

please note all TVFP email
addresses have changed
new email below

[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to