Do you have a hose connection on the 1st floor landing of the remote standpipe stairwell in addition to the one at the exit passageway door? And is there access to occupiable areas on the first floor from the passageway or stairwell?
Obviously, two or more hose connections supplied by a feed main on a single floor is a horizontal standpipe by definition, but it would seem to me that in this type of egress system that would be redundant or not of value depending on where a firefighter would be going with the water after connection to one or the other hose connection. The foregoing does not represent any opinion or interpretation of the standard on behalf of NFPA or the NFPA 14 Technical Committee. [cid:[email protected]] Steve Leyton, President T | 619.255.8964 x 102 | www.protectiondesign.com<http://www.protectiondesign.com/> 2851 Camino Del Rio South | Suite 210 | San Diego, CA 92108 Fire Protection System Design | Consulting | Planning | Training From: Chris Wilson [mailto:[email protected]] Sent: Friday, May 10, 2024 7:42 AM To: [email protected] Subject: [Sprinklerforum] Standpipe NFPA14 2019 To all, I have a 4 story building with 2 exit stairways I am installing a class I manual wet standpipe combination sprinkler system. The remote stair is on the interior of the building and has a rated exit passageway on the first floor that is 73' long. I am placing all hose valves on the main floor landings and one a the exit door of the exit passage way. I am planning on calculating 500 gpm from the remote stand pipe and 250 for the 2nd standpipe. The exit passage way hose connection will be fed by a 2/12 lateral pipe fed from the 4" horizontal supply to the remote standpipe as it pass by the exit passageway. Do I need to include an additional 250 gpm in my calcs at the hose valve at the exit passageway? Thanks Christopher S. Wilson SET Project Design Manager Treasure Valley Fire Protection 2731 S. Saturn Way Boise, ID 83709 Phone: 208-362-1888 Fax: 208-362-2207 please note all TVFP email addresses have changed new email below [email protected]<mailto:[email protected]>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]