If you use the dropmaster properly you can get nearly all of the water out to 
the point that when you pull a head you get just drops of water. I would do it 
with the antifreeze, fill and repeat a couple of times to make certain there 
wasn't enough antifreeze left to create a problem with mixing. We would use the 
DM and then pull a few heads to see what we had and if it was as empty as we 
expect, I would not have a problem refilling it with new.
________________________________
From: Caleb Brogan <[email protected]>
Sent: Thursday, March 21, 2024 12:55 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Mixed antifreeze types


Dropmasters work great, but I wouldn’t rely on it to pull all the existing 
antifreeze out of every drop just by pulling a few. I have no idea on the 
potential mixing of the two solutions, but my personal opinion would be that 
Freezemaster is pretty expensive. The customer is paying for it, might as well 
make sure it’s all new. It shouldn’t take more than a day or two to drain 100 
drops with a couple guys working  (if the system drains well), so I would take 
the time to pull them out and make sure it’s clear. I haven’t tried to use a 
dropmaster on antifreeze though but with water it will suck a head into the RC 
from a foot away if it is working correctly.



Thanks,

Caleb



Caleb Brogan | Sprinkler Systems Designer
OH# 54-25-4815 & NICET# 147230
KOORSEN FIRE & SECURITY
727 Manor Park Dr, Columbus, OH 43228
P 614.853.5665 | Ext. 6512 | M 614.867.6791
[email protected]<mailto:[email protected]> | 
www.koorsen.com<http://www.koorsen.com>

24x7x365 Service: 614.878.2228 | [email protected]

From: Fpdcdesign <[email protected]>
Sent: Thursday, March 21, 2024 1:28 PM
To: SprinklerForum <[email protected]>
Subject: [Sprinklerforum] Mixed antifreeze types



I have a client with a rather large (330 gallon) antifreeze system that is 
looking to upgrade to an approved solution. There are approximately 100 pendent 
sprinklers on either straight drops or swing joints. The contractor has 
proposed pulling a few drops and using a Dropmaster to try and drain the rest 
of them. I have no personal knowledge of how effective a Dropmaster is. Would 
using this be acceptable? Is there a way to tell if it worked? If there was a 
small amount of glycerine solution remaining, would that be a compatibility 
issue with Freezemaster? I will probably contact Lubrizol as well but am also 
looking for experience.



Todd G Williams, PE

Fire Protection Design/Consulting

Stonington, CT

860-535-2080<tel:860-535-2080> (ofc)

860-554-7054<tel:860-554-7054>  (fax)

860-608-4559<tel:860-608-4559> (cell)
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to