In our area they don’t make us perform the test but we are required to have a 
sign at the fdc with the flow and pressure needed to get the 100 psi at the 
remote hose conecttion.

Christopher S. Wilson SET
Project Design Manager
Treasure Valley Fire Protection
2731 S. Saturn Way
Boise, ID 83709
Phone:  208-362-1888
Fax: 208-362-2207

please note all TVFP email
addresses have changed
new email below

[email protected]<mailto:[email protected]>

From: Steve Mackinnon <[email protected]>
Sent: Thursday, March 7, 2024 7:08 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Manual Wet Standpipe Inspection

Good morning,

We’ve found it all depends on the district and individual AHJ…

We do a number of manual wet/dry standpipes in our area and each one comes with 
it’s own challenges.

One of my colleagues just invested in a used fire truck figuring the best 
course of action is to be over prepared than under.

Another company gives “donations” to the local Fire Dept. to come and flow the 
standpipe at test time (this can get expensive over time).

But we always provide a hydraulic calculation for the required flow beforehand.

I found most Fire Pump operators start with 90-100 psi and increase by 10 psi 
until we reach the desired flow and pressure on the roof.

From: Chris Dorn 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, March 6, 2024 6:53 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Manual Wet Standpipe Inspection

We have been required to perform a flow test using the city fire truck and the 
top two hose valves. I only did it once but the firemen seemed excited to do 
it. I have been required to run some quick calculations to tell them what 
pressure the pumper needed to provide at the FDC to give them the pressure they 
wanted at the top of a standpipe pretty much every one we do.

Christopher Dorn
Dorn Fire Protection LLC
4132 Dumont Street #4
Cincinnati, Ohio 45226
(513) 295-2499

On Mar 6, 2024, at 5:06 PM, Anthony Carrizosa 
<[email protected]<mailto:[email protected]>> wrote:

Derik,
NFPA 25 states flow tests 6.3.1 Shall be conducted every 5 years on all 
automatic standpipe systems.. your system is not automatic but manual. Since it 
is under water pressure at all times no need for a hydro test either.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
<image005.jpg>
https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>

From: Derik Rich <[email protected]<mailto:[email protected]>>
Sent: Wednesday, March 6, 2024 1:53 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Manual Wet Standpipe Inspection

Looking for some guidance on flow testing a manual wet standpipe. I have been 
told; A. You don’t have to flow test. B. Perform flow test and calculate 
assistance needed. C. You need to do a proper test with a pumper truck. The 
only thing I can find in 25 is that no hydrostatic test is required on manual 
wet. Can anybody steer me in the right direction? Thanks,

<image006.png>
Derik Rich
Estimator


O:
801-281-0746
C:
801-231-6375
A:
1015 S. 3600 W. SLC, UT 84104
E:
[email protected]<mailto:[email protected]>
<image007.png><https://www.facebook.com/certfs/>

<image008.png><https://www.linkedin.com/company/14776965/>

<image009.png><https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fcertfs.com%2f&c=E,1,wEIMwwzvZLvEOpO3oTJ9O3LcWCmB_bKGjKeRHx3AqpZFUGqxltzjLXcLL2QdS7_mib0mFs_oH-4geaUkpKI8cLXyYhgAH5J1R_lhzmATVDBZFFmYtVXuxOQ,&typo=1>




_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]