Derik, NFPA 25 states flow tests 6.3.1 Shall be conducted every 5 years on all automatic standpipe systems.. your system is not automatic but manual. Since it is under water pressure at all times no need for a hydro test either.
Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:[email protected]] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1> From: Derik Rich <[email protected]> Sent: Wednesday, March 6, 2024 1:53 PM To: [email protected] Subject: [Sprinklerforum] Manual Wet Standpipe Inspection Looking for some guidance on flow testing a manual wet standpipe. I have been told; A. You don't have to flow test. B. Perform flow test and calculate assistance needed. C. You need to do a proper test with a pumper truck. The only thing I can find in 25 is that no hydrostatic test is required on manual wet. Can anybody steer me in the right direction? Thanks, [cid:[email protected]] Derik Rich Estimator O: 801-281-0746 C: 801-231-6375 A: 1015 S. 3600 W. SLC, UT 84104 E: [email protected]<mailto:[email protected]> [facebook]<https://www.facebook.com/certfs/> [linkedin]<https://www.linkedin.com/company/14776965/> [website]<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fcertfs.com%2f&c=E,1,wEIMwwzvZLvEOpO3oTJ9O3LcWCmB_bKGjKeRHx3AqpZFUGqxltzjLXcLL2QdS7_mib0mFs_oH-4geaUkpKI8cLXyYhgAH5J1R_lhzmATVDBZFFmYtVXuxOQ,&typo=1>
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]