We did end up going to EH1 in order to avoid trying to fight with the plan
reviewer. I was thinking along the same lines as Ken - NFPA 12 (2016)
23.4.4.2.4 is specifically in the area/density section when it comes to
adding flow for heads that are not present.

I had just never encountered a comment like this before.

On Thu, Feb 8, 2024 at 11:58 AM Anthony Carrizosa <
[email protected]> wrote:

> Can you use the Room Design method? Look at NFPA 13 – 2016 – section
> 11.2.3.3.4 and then 11.2.3.1.4 (2) looks like if the room is smaller than
> the required area of an EH1 @2500 sqft then use the size of the room @ the
> required density for the 2500 sqft. ( .30/2500) or .30/300 for your room.
>
>
>
> *Anthony Carrizosa *
>
> Project Manager *| *Fire Protection
>
> 7855 S 206th St Kent, WA 98032
>
> Cell: *206-679-5283* | Office Dir: *253-341-4593*
>
> https://archerconstruction.com
> <https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1>
>
>
>
> *From:* Matt Grise <[email protected]>
> *Sent:* Thursday, February 8, 2024 8:54 AM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Small ESFR system
>
>
>
> We are looking at an auto repair facility that has a very small tire
> storage room (apx 300sf). The tire storage space is open on one side to the
> misc parts storage area (short-shelf OH2). Our thought was to protect the
> tire storage space with a small ESFR system that extends 15' into the misc
> parts storage area. The other 3 sides of the tire storage room are CMU and
> extend to the deck.
>
>
>
> Even with the 15' extension into the lesser hazard area, there are only 6
> ESFR sprinklers needed. (2 heads on 3 lines) = 540sf.
>
>
>
> Based on the annex commentary in NFPA 13 2016 A11.1.2, our plan was to
> calc the 6 esfr heads (the full higher-hazard area plus 15' = 540sf) along
> with 960sf  at .2gpm/sf to round out the larger of the two operating areas.
>
>
>
>
>
> We received some pushback because there is no ESFR design criteria that
> only uses 6 heads, so the plan reviewer was concerned that we were not
> following the 12-head design for an ESFR system.
>
>
>
> There was a suggestion that we should pretend there were 12 heads and calc
> a 12 head area (even though 6 would never be installed).I figured that
> since we were calculating ALL of the ESFR heads in the building, that would
> be ok.
>
>
>
> Has anyone seen anything like this before? Any thoughts?
>
>
>
> Thanks!
>
>
>
> Matt Grise
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>