Sorry, i meant 23.4.4.2.4 not 23.4.4.2.3

Benjamin Young


On Thu, Feb 8, 2024 at 12:23 PM Ben Young <[email protected]> wrote:

> In the 2016 edition, check out sections 23.4.4.2.3 and 23.4.4.2.5
>
> Use those to add phantom flow based on the minimum flow from 12 sprinklers.
>
> It's a variation on the theme but it should satisfy the ahj.
>
>
> Benjamin Young
>
>
> On Thu, Feb 8, 2024 at 11:55 AM Matt Grise <[email protected]> wrote:
>
>> We are looking at an auto repair facility that has a very small tire
>> storage room (apx 300sf). The tire storage space is open on one side to the
>> misc parts storage area (short-shelf OH2). Our thought was to protect the
>> tire storage space with a small ESFR system that extends 15' into the misc
>> parts storage area. The other 3 sides of the tire storage room are CMU and
>> extend to the deck.
>>
>> Even with the 15' extension into the lesser hazard area, there are only 6
>> ESFR sprinklers needed. (2 heads on 3 lines) = 540sf.
>>
>> Based on the annex commentary in NFPA 13 2016 A11.1.2, our plan was to
>> calc the 6 esfr heads (the full higher-hazard area plus 15' = 540sf) along
>> with 960sf  at .2gpm/sf to round out the larger of the two operating areas.
>>
>>
>> We received some pushback because there is no ESFR design criteria that
>> only uses 6 heads, so the plan reviewer was concerned that we were not
>> following the 12-head design for an ESFR system.
>>
>> There was a suggestion that we should pretend there were 12 heads and
>> calc a 12 head area (even though 6 would never be installed).I figured that
>> since we were calculating ALL of the ESFR heads in the building, that would
>> be ok.
>>
>> Has anyone seen anything like this before? Any thoughts?
>>
>> Thanks!
>>
>> Matt Grise
>>
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to