You can tie-in multiple low point drains on dry systems together. it's actually 
a "shall" for multiple branchlines.
NFPA 13 2013 & 2016
8.16.2.5.3.6 Tie-in drains shall be provided for multiple adjacent trapped 
branch pipes and shall be only 1 in. (25 mm).Tie-in drain lines shall be 
pitched a minimum of 1⁄2 in. per 10 ft(4 mm/m).
This section was moved to 16.10.5.3.6 in 2019.

I don't see any reason you couldn't provide tie-in drains post drum drip either.

Jamie Seidl

On Wed, Jan 31, 2024 at 4:53 PM Taylor Schumacher 
<[email protected]<mailto:[email protected]>> wrote:
I remember seeing something that says you cannot combine dry system drains 
together, but I cannot find it. FWIW, this would be post drum drips.

Thanks,


Taylor Schumacher